DMD0529

CTRUNPOS - CTRIO Run Position Mode


The CTRIO Run Position Mode (CTRUNPOS) instruction is used to load and run one of the pre-configured Pulse Profiles in the System Configuration for the CTRIO.

 

The red triangle in the upper left corner indicates the CTRIO Run Position Mode (CTRUNPOS) is a Fully Asynchronous instruction.

 

Note: The CTRUNPOS instruction can be used with both the CTRIO and CTRIO2 module.

 

Inputs:

The first input (E/R) in the Enable / Reset input. When this input logic is ON the specified Pulse Profile will be loaded, and the Output will be enabled (.OutputEnabled = ON) and the move will be executed.

 

The second input (DIR) is the Direction. This input has different effects on the CTRIO output depending on the pulse profile specified by the Position File Number parameter.

 

DEVICE

CTRIO/CTRIO2 PULSE PROFILE

EFFECT

CTRIO2

Trapezoid
S-Curve
Symmetrical S-Curve
Home Search
Free Form
Trapezoid w/Limits (CTRIO2)

If the DIR input is OFF when the E/R input comes ON, the CTRIO2 will generate pulses for clockwise (positive) direction.
If the DIR input is ON when the E/R input comes ON, the CTRIO2 will generate pulses for counter-clockwise (negative) direction.

Trapezoid Plus (CTRIO2)

The DIR input has no effect. The direction is determined by the sign of the Trapezoid-Plus Target Pos. parameter.
If positive, the CTRIO2 will generate pulses for clockwise (positive) direction.
If negative, the CTRIO2 will generate pulses for counter-clockwise (negative) direction.

CTRIO

Trapezoid
S-Curve
Symmetrical S-Curve
Home Search
Free Form

If the DIR input is OFF when the E/R input comes ON, the CTRIO will generate pulses for clockwise (positive) direction.
If the DIR input is ON when the E/R input comes ON, the CTRIO will generate pulses for counter-clockwise (negative) direction.

Trapezoid Plus (CTRIO2)
Trapezoid w/Limits (CTRIO2)

Note: Attempting to use these pulse profiles with the CTRIO will result in an Error 103 (see chart below).

 

 

The third input (SUS) is the Suspend input. This input has different effects on the CTRIO output depending on the pulse profile specified by the Position File Number parameter:

 

DEVICE

CTRIO/CTRIO2 PULSE PROFILE

EFFECT

CTRIO2

Trapezoid
S-Curve
Symmetrical S-Curve
Home Search
Free Form

When SUS input comes ON the CTRIO2 will abruptly stop emitting output pulses.

When SUS input returns to OFF the CTRIO2 will abruptly start emitting the remaining output pulses.

(Refer to the Abrupt Suspend picture below)

Trapezoid Plus (CTRIO2)
Trapezoid w/Limits (CTRIO2)

When SUS input comes ON, the CTRIO2 will ramp down to zero using the Decel Rate specified in the pulse profile.
When SUS input returns to OFF the CTRIO2 will ramp up to the Maximum Freq using the Accel Rate both which are specified in the pulse profile.

(Refer to the Deceleration Suspend picture below)

CTRIO

Trapezoid
S-Curve
Symmetrical S-Curve
Home Search
Free Form

When SUS input comes ON the CTRIO will abruptly stop emitting output pulses.

When SUS input returns to OFF the CTRIO will abruptly start emitting the remaining output pulses.

(Refer to the Abrupt Suspend picture below)

Trapezoid Plus (CTRIO2)
Trapezoid w/Limits (CTRIO2)

Note: Attempting to use these pulse profiles with the CTRIO will result in an Error 103 (see chart below).

 

Abrupt Suspend

 

Deceleration Suspend

 

Parameters:

Note: Use the F9 key (Element Browser) at any time to see a complete list of the memory locations that are valid in the current field of the instruction.

 

Pulse Output Device - designates which of the pre-configured CTRIO Devices to interact with. Before this instruction can select a Pulse Output Device, a CTRIO Device must be configured with at least one of its output channels setup for Pulse/Direction or CW/CCW pulse output mode. Part of the configuration for a device is assigning a name to the device. It is that name which will show up in the Pulse Output Device selection drop-down menu. For more information on configuring CTRIO devices go to the Module Configuration Section under System Configuration.

 

Note: no devices available - indicates that there are no CTRIO Devices that have been pre-configured to perform this instruction.

 

Pulse Output Structure -  this field displays the name of the Pulse Output Structure that will be used by this instruction. This structure was created when the CTRIO module was configured during the Module Configuration phase.

 

Position File Number - designates which of the pre-configured Pulse Profiles to Run. The profile can be specified in one of the following three ways:
 

  • Fixed File - displays a list of the pre-configured Pulse Profiles that were read from the CTRIO module during the Module Configuration phase. Select the desired profile from the list. Available Profiles:

 

PROFILE

(Silver text indicates the profile cannot be used with CTRUNPOS)

CTRIO

CTRIO2

Trapezoid

Yes

Yes

S-Curve

Yes

Yes

Symmetrical S-Curve

Yes

Yes

Dynamic Positioning

 

 

Dynamic Velocity

 

 

Home Search

Yes

Yes

Free Form

Yes

Yes

Dynamic Positioning Plus (CTRIO2)

 

 

Trapezoid Plus (CTRIO2)

No

Yes

Trapezoid w/Limits (CTRIO2)

No

Yes

 

  • Variable File Number - designates a location where the Pulse Profile number will be read. This can be any readable numeric location.
     

Optional Target Position - Note: this parameter can only be used with a Trapezoid Plus or the Trapezoid w/Limits profile in the CTRIO2 module - specifies the target position count value. This can be any positive or negative constant value or any readable numeric location. If this parameter is greater than the current position (.OutputPosition), pulses for a clockwise move are emitted. If this parameter is less than the current position (.OutputPosition), pulses for a counter-clockwise move are emitted.

 

On Success - designates which of the following actions to take if the CTRIO Run Position Mode operation is successful, that is, the specified Pulse Profile is loaded, and that Pulse Profile has run to completion.

 

  • SET BIT - The specific BIT location will be turned OFF when the CTRIO Run Position Mode (CTRUNPOS) instruction is first enabled, and then SET ON if the operation is successful. This value can be any writable bit location.
     

  • JMP to Stage - JMP to the specified Stage. The target Stage must be in the same Program code block as the CTRIO Run Position Mode (CTRUNPOS) instruction, you cannot specify a Stage in a different Program code block. This selection will function like a standalone Jump to Stage instruction. Click here for more information on the Jump To Stage instruction.

 

On Error - designates which of the following two actions to take if the CTRIO Run Position Mode operation is unsuccessful. For example if the specified Pulse Profile is missing, or the specified Profile number is the wrong type for a Pulse Output.

 

  • SET BIT - The specific BIT location will be turned OFF when the CTRIO Run Position Mode (CTRUNPOS) instruction is first enabled, and then SET ON if the operation is unsuccessful. This value can be any writable bit location.
     

  • JMP to Stage - JMP to the specified Stage. The target Stage must be in the same Program code block as the CTRIO Run Position Mode (CTRUNPOS) instruction, you cannot specify a Stage in a different Program code block. This selection will function the same as a standalone Jump to Stage instruction. Click here for more information on the Jump To Stage instruction.

 

Note: any time the On Error condition occurs, the CTRIO generates an Error Code that can be read in the <Module Name>.ErrorCode (Module Name is the name assigned to the CTRIO in the Module Configuration). The List of Error Code values (in decimal) follows:

 

Error Code

Description

000

No Error

100

Specified command code is unknown or unsupported

101

File number not found in the file system

102

File type is incorrect for specified output function

103

Profile type is unknown

104

Specified input is not configured as a limit on this output

105

Specified limit input edge is out of range

106

Specified input function is unconfigured or invalid

107

Specified input function number is out of range

108

Specified preset function is invalid

109

Preset table is full

110

Specified Table entry is out of range

111

Specified register number is out of range

112

Specified register is an unconfigured input or output

113

Specified output is not configured as a limit on this output

114

Specified preset function invalid in PLS table

115

Specified PLS function invalid in preset table

116

PLS table entries overlap

117

Attempted to use axis function when pulse output is not in Axis Mode

118

Specified output isn't a pulse output

 


Status Display:

The Status display of the CTRIO Run Position Mode (CTRUNPOS) instruction shows:

 

  • Values: Target Position or Optional Target Position if a CTRIO2 Trapezoid Plus or Trapezoid w/Limits profile is being used.
     

  • Highlight: .OutputEnabled, .OutputActive, .Direction, .OutputSuspended, .OutputStalled, bits
     

  • ON/OFF: On Success, On Error bits
     


CTRIO Structure Field Care-Abouts:

The following is a list of the"dot" fields of the CTRIO structure that are programmatically used with the CTRIO Run Position Mode (CTRUNPOS) instruction. To see a complete listing of all CTRIO structures and members, goto the Project Browser --> Configuration --> Memory --> I/O --> Specialty.

 

COLOR KEY

Blue: CTRIO Input

Maroon: CTRIO Output

Black: CTRIO Module

Silver: Not used for this instruction

 

Note: The red "x" is the digit 0, 1, 2, or 3.

 

CTRIO_000

CTRUNPOS

MEMBER

R/W

TYPE

DESCRIPTION

_CxFx.AtResetValue

RO

Bit

ON if CxFx count is at reset value

_CxFx.CaptureComplete

 

 

 

_CxFx.CapturedStart

 

 

 

_CxFx.CountCaptured

 

 

 

_CxFx.EnableCapture

 

 

 

_CxFx.fReg1

RO

Dword

If floating-point scaling is configured for CxFx in CTRIO2: Floating-point scaled value; otherwise, number has no meaning

_CxFx.fReg2

 

 

 

_CxFx.iReg1

RO

Dword

If integer or BCD scaling is configured for CxFx in CTRIO2: Signed-integer or BCD scaled value; otherwise, signed-integer raw count

_CxFx.iReg2

RO

Dword

If any scaling is configured for CxFx in CTRIO2: Signed-integer raw count; otherwise, number has no meaning

_CxFx.Output

 

 

 

_CxFx.Reset

R/W

Bit

Set ON to reset CxFx count

_CxFx.Timeout

 

 

 

_Outx.AtPosition

 

 

 

_Outx.AtVelocity

 

 

 

_Outx.Direction

RO

Bit

If using CTRIO2: ON when motor is moving counter-clockwise

_Outx.EnableOutput

 

 

 

_Outx.GotoPosition

 

 

 

_Outx.Output

 

 

 

_Outx.OutputActive

RO

Bit

ON when CTRIO output is generating pulses

_Outx.OutputEnabled

RO

Bit

ON when CTRIO output has been enabled

_Outx.OutputPosition

RO

Dword

Output raw position, or if Position File Number is Trapezoid Plus or Trapezoid w/Limits profile (CTRIO2 only) with Use Encoder for Position, then: CTRIO2 output position (scaled by the profile's Scale Factor)

_Outx.OutputStalled

RO

Bit

ON if CTRIO output cannot generate pulses because its scantime is too high

_Outx.OutputSuspended

RO

Bit

ON when CTRIO output has been suspended

_Outx.OutputVelocity

RO

Dword

If using CTRIO2: Current pulses per second rate being output by the CTRIO2

_Outx.TableComplete

 

 

 

.ErrorCode

RO

Word

Last CTRIO error code

.Mode

RO

Word

Indicates CTRIO mode: 2 = RUN; 1 = PROGRAM

.ScanTime

RO

Word

CTRIO scantime in microseconds

.MaxScanTime

RO

Word

Maximum CTRIO scantime in microseconds

.InputState

RO

Word

Upper byte is not used. Lower byte's nibbles indicate CTRIO's channel's input's state in order: .ChxD, .ChxC, .ChxB, .ChxA. It is a composite of these members

.OutputState

RO

Word

Each nibble indicates a CTRIO output configuration and state: .OutxType, .OutxDiscOn, .OutxDiscEnabled, .OutxPulseActive. It is a composite of these members

.ChxA

RO

Bit

ON when CTRIO Channel x Input A is ON

.ChxB

RO

Bit

ON when CTRIO Channel x Input B is ON

.ChxC

RO

Bit

ON when CTRIO Channel x Input C is ON

.ChxD

RO

Bit

ON when CTRIO Channel x Input D is ON

.OutxType

RO

Bit

Configuration: ON if CTRIO output x is configured for pulse output

.OutxDiscOn

RO

Bit

Status: ON if CTRIO output x logic is ON (if output x is enabled then the physical output will also be ON)

.OutxDiscEnabled

RO

Bit

Configuration: ON if CTRIO output x is configured for discrete output

.OutxPulseActive

RO

Bit

Status: ON if CTRIO output x is generating pulses

 


See Also:


Example 1 of 2:

Description of a Typical CTRIO Run Position Mode (CTRUNPOS) Stage Diagram:

To the right is a stage diagram of a simple sequence control that would home a motor to position and then allow any number of moves using the CTRUNPOS instruction, a CTRIO2 and a predefined Trapezoid PLUS Pulse Profile.

 

Initially the Home stage homes the motor. When this is complete it transitions to the Zero stage.

 

The Zero stage resets the CTRIO2 output position to zero (0) after the homing and then transitions to the Position stage.

 

The Position stage positions the motor depending upon a variable. When this position is reached it transitions to the InPos stage where the decision is made as to whether this was the last move or not.

 

The InPos stage is where the decision is made as to whether there is another position to move to, or if the sequence is complete. If it was not the last move, a new value is loaded in the position variable and transition is made back to the Position stage. If it was the last move then transition is made to the Stop stage.

 

The Stop stage simply exits the Program code block.

 

Description of a Typical CTRIO Run Position Mode (CTRUNPOS) Stage Ladder:

To the right is the ladder equivalent of the above stage diagram that uses the CTRUNPOS instruction which will home a stepper motor attached to the CTRIO2's pulse output and then allow any number of relative moves to subsequent positions and then stop.

 

Note: Since CTRIO2 pulse profiles are being used, this example cannot be used for a CTRIO module.

 

This example presupposes the existence of the following System Configuration for the CTRIO2 (PLC --> System Configuration --> Module Configuration(s) --> CTRIO_000 -->):

  • Configure I/O -->

    • Outputs --> Out0 --> Pulse (Step/Dir).

    • Inputs -->

      • A --> Quad Counter.

      • D --> Limit Out 0.

  • Pulse Profiles -->

    • File 15 --> Trapezoid w/Limits -->
        Decel Trigger: Limit Switch on Ch1D, Event: Rising Edge
        Stop Trigger: Position
        
      Values for Minimum Freq, Maximum Freq, Accel Rate, & Decel Rate
        Use Encoder for Position: Encoder Input: Channel 1
             
      Values for Scale Factor & Deadband

    • File 12 --> Trapezoid Plus -->
        Values for Minimum Freq, Maximum Freq, Accel Rate, Decel Rate
        Use Encoder for Position: Encoder Input: Channel 1
        
      Values for Scale Factor & Deadband

  • A stepper motor is wired to CTRIO2 Output 0 and Output 1.

  • A quadrature encoder associated with the stepper motor is wired to CTRIO2 Input A and Input B.

  • A normally open proximity sensor is wired to CTRIO2 Input D.

 

Home is the initial state which waits for HomeStart bit to come ON. The HomeDIR bit must be turned ON if home position is to be searched for in the counter-clockwise direction, or left OFF if home position is in the clockwise direction. This bit must be in the desired state before HomeStart bit is turned ON. The HomeSUS bit can be used to temporarily suspend the home-search. When the HomeStart bit comes ON, if there is an error the CTRUNPOS instruction will immediately transition to the ErrorHandler stage, where ladder logic should exist (not shown here) to handle the error (e.g. read $CTRIO_000.ErrorCode). If no error occurs the CTRUNPOS loads the Trapezoid w/Limits profile and begins to accelerate toward maximum frequency (according to the pulse profile's parameter values) searching for a signal on the CTRIO2's Input D. As configured in the profile, when the CTRIO2 sees the signal on Input D, the profile decelerates to the HomePosition value. When complete the CTRUNPOS transitions to the Zero stage.

 

Zero stage uses the CTREGWR instruction to write a zero (0) to the output position ($CTRIO_000_Out0.OutputPosition) and clears the quadrature encoder count by turning ON the $CTRIO_000_C1F1.Reset bit. If there is an error, transition is made to the ErrorHandler stage. If it completes without error, transition is made to the Position stage. When the Zero stage is exited, it will turn the $CTRIO_000_C1F1.Reset bit back OFF so the quadrature counter is free to count.

 

Position stage waits for PositionRun bit to come ON. Since the Position File Number being used is a Trapezoid Plus profile, the DIR input on the CTRUNPOS instruction has no effect (see chart above), thus, it is set to $Off. The PositionSUS bit can be used to temporarily suspend the move if necessary. Before the PositionRun bit is turned ON, the TargetPosition must be set to the desired relative position. If reverse motion is desired a negative number must be used. When the PositionRun bit comes ON, if there is an error the CTRUNPOS instruction will immediately transition to the ErrorHandler stage. If no error occurs the CTRUNPOS loads the Trapezoid Plus profile and begins to accelerate toward maximum frequency (according to the pulse profile's parameter values) and decelerate to the TargetPosition value position until it is reached. When the position is reached the CTRUNPOS instruction transitions to the InPos stage.

 

In the InPos stage the decision is made as to whether this was the last move or not. If there are more relative moves to be executed, a new relative position value must be written to TargetPosition and then the NextMove bit must be turned ON. Turning the NextMove bit ON, will turn itself OFF (to prevent multiple moves) and transition back to the Position stage for another execution of the CTRUNPOS instruction. If this was the last move, the Done bit is turned ON and the Program code block is exited.


Example 2 of 2:


Copyright Host Engineering, Inc. ALL RIGHTS RESERVED