Topic: DMD0519

CTAXDYNP - CTRIO2 Axis Run Dynamic Position Mode


Note: The CTAXDYNP instruction can only be used with the CTRIO2 module.

 

The CTRIO2 Axis Run Dynamic Position Mode (CTAXDYNP) instruction is used to put the Pulse Output Device into Dynamic Position Mode, allowing successive moves to be easily commanded. Once in Dynamic Position Mode, moves are commanded by changing the Target Position value and setting (one-shot) the .GotoPosition bit for the Pulse Output Device. The moves will execute using the parameters defined in the CTRIO2 Axis Configuration (CTAXCFG) instruction executed before the CTAXDYNP. Click here for more information on the Axis Configuration instruction.

 

The red triangle in the upper left corner indicates the CTRIO2 Axis Run Dynamic Position Mode (CTAXDYNP) is a Fully Asynchronous instruction.

 

Inputs:

The first input (E/R) is the Enable / Reset input. When this input logic comes ON the Pulse Output Device is placed in the "Dynamic Positioning Mode", the current position value will be set to 0 or maintained (i.e. .OutputPosition) and the Output will be enabled (.OutputEnabled = ON). It must remain ON until all desired positions have been reached. When this input logic goes OFF the Pulse Output Device is removed from "Dynamic Positioning Mode", the Output will be disabled (.OutputEnabled = OFF) and the On Success or On Error bits are set.

 

The second input (SUS) is the Suspend input.

When this input logic transitions ON, the CTRIO2 will ramp down to zero using the Deceleration Rate specified in the Axis Configuration (CTAXCFG). Click here for more information on the Axis Configuration instruction. No additional pulses will be emitted as long as this input remains ON.

When this input logic transitions OFF, the CTRIO2 will ramp up to the Maximum Frequency at Acceleration Rate specified in the Axis Configuration (CTAXCFG) toward the Target Position. Click here for more information on the Axis Configuration instruction.

 

Parameters:

Note: Use the F9 key (Element Browser) or Down-Arrow key (Auto-Complete) at any time to see a complete list of the memory locations that are valid in the current field of the instruction.

 

Pulse Output Device - designates which of the pre-configured CTRIO2 Devices to interact with. Before this instruction can select a Pulse Output Device, a CTRIO2 must be configured with at least one of its output channels setup for Pulse/Direction or CW/CCW pulse output mode.

 

Part of the configuration for a device is assigning a name to the device. It is that name which will show up in the Pulse Output Device selection drop-down menu. For more information on configuring CTRIO2 devices go to the Module Configuration Section under System Configuration.

 

Note: no devices available - indicates that there are no CTRIO2 Devices that have been pre-configured to perform this instruction. Selecting 'create module' from the drop-down list will invoke the Create New Module Configuration dialog.

 

Note: create module - Selecting this will immediately pull up the System Configuration and allow the creation of a new module (see Module Configuration Section under System Configuration.)

 

Pulse Output Structure - This field displays the name of the Pulse Output Structure that will be used by this instruction. This structure was created when the CTRIO2 module was configured during the Module Configuration phase.

 


Current Position - this option specifies what action to take regarding the current position value when the instruction is enabled

 

  • Zero-out - initialize the current position value for the Pulse Output to 0, .OutputPosition will be set to 0
     

  • Maintain value - leaves the current position value for the Pulse Output intact, .OutputPosition will remain at whatever value it has

 


 

Target Position - specifies the pulse count of the target position. The direction (clockwise or counter-clockwise) is inferred from the difference between the Target Position and the current position (.OutputPosition), that is, if the Target Position is greater than the current position, pulses for a clockwise move are emitted; if the Target Position is less than the current position, pulses for a counter-clockwise move are emitted. This can be any positive or negative constant value or any readable numeric location.

 


 

On Success - designates which of the following actions to take at the conclusion of a CTRIO2 Axis Run Dynamic Position Mode operation.
 

Note: This selection DOES NOT indicate that the Target Position has been reached, use the .AtPosition for that information.

 

  • SET BIT - The specific BIT location will be turned OFF when the CTRIO2 Axis Run Dynamic Position Mode (CTAXDYNP) instruction is first enabled, and then SET ON if the operation is successful. This value can be any writable bit location.
     

  • JMP to Stage - JMP to the specified Stage. The target Stage must be in the same Program code block as the CTRIO2 Axis Run Dynamic Position Mode (CTAXDYNP) instruction, you cannot specify a Stage in a different Program code block. This selection will function like a standalone Jump to Stage instruction. Click here for more information on the Jump To Stage instruction.

 

On Error - designates which of the following two actions to take if the CTRIO2 Axis Run Dynamic Position Mode operation was unsuccessful. For example if this instruction tries to target a CTRIO module (not a CTRIO2), or if the specified output device is not configured as a Pulse Output.
 

  • SET BIT - The specific BIT location will be turned OFF when the CTRIO2 Axis Run Dynamic Position Mode (CTAXDYNP) is first enabled, and then SET ON if the operation is unsuccessful. This value can be any writable bit location.
     

  • JMP to Stage - JMP to the specified Stage. The target Stage must be in the same Program code block as the CTRIO2 Axis Run Dynamic Position Mode (CTAXDYNP) instruction, you cannot specify a Stage in a different Program code block. This selection will function the same as a standalone Jump to Stage instruction. Click here for more information on the Jump To Stage instruction.

 

Note: any time the On Error condition occurs, the CTRIO2 generates an Error Code that can be read in the <Module Name>.ErrorCode (Module Name is the name assigned to the CTRIO2 in the Module Configuration). The List of Error Code values (in decimal) follows:

 

Error Code

Description

000

No Error

100

Specified command code is unknown or unsupported

101

File number not found in the file system

102

File type is incorrect for specified output function

103

Profile type is unknown

104

Specified input is not configured as a limit on this output

105

Specified limit input edge is out of range

106

Specified input function is unconfigured or invalid

107

Specified input function number is out of range

108

Specified preset function is invalid

109

Preset table is full

110

Specified Table entry is out of range

111

Specified register number is out of range

112

Specified register is an unconfigured input or output

113

Specified output is not configured as a limit on this output

114

Specified preset function invalid in PLS table

115

Specified PLS function invalid in preset table

116

PLS table entries overlap

117

Attempted to use axis function when pulse output is not in Axis Mode

118

Specified output isn't a pulse output

 


Status Display:

The Status display of the CTRIO2 Axis Run Dynamic Position Mode (CTAXDYNP) instruction shows:

 

  • Values: .OutputPosition, Target Position, Current Position
     

  • Highlight: .OutputEnabled, .OutputActive, .AtPosition, .OutputSuspended, .OutputStalled, .GotoPosition bits
     

  • ON/OFF: On Success, On Error bits

 


CTRIO2 Structure Field Care-Abouts:

The following is a list of the"dot" fields of the CTRIO2 structure that are programmatically used with the CTRIO2 Axis Run Dynamic Position Mode (CTAXDYNP) instruction. To see a complete listing of all CTRIO structures and members, goto the Project Browser --> Configuration --> Memory --> I/O --> Specialty.

 

COLOR KEY

Blue: CTRIO2 Input

Maroon: CTRIO2 Output

Black: CTRIO2 Module

Silver: Not used for this instruction

 

Note: The red "x" is the digit 0, 1, 2, or 3.

 

CTRIO_000

CTAXDYNP

MEMBER

R/W

TYPE

DESCRIPTION

_CxFx.AtResetValue

RO

Bit

ON if CxFx count is at reset value

_CxFx.CaptureComplete

 

 

 

_CxFx.CapturedStart

 

 

 

_CxFx.CountCaptured

 

 

 

_CxFx.EnableCapture

 

 

 

_CxFx.fReg1

RO

Dword

If floating-point scaling is configured for CxFx in CTRIO2: Floating-point scaled value; otherwise, number has no meaning

_CxFx.fReg2

 

 

 

_CxFx.iReg1

RO

Dword

If integer or BCD scaling is configured for CxFx in CTRIO2: Signed-integer or BCD scaled value; otherwise, signed-integer raw count

_CxFx.iReg2

RO

Dword

If any scaling is configured for CxFx in CTRIO2: Signed-integer raw count; otherwise, number has no meaning

_CxFx.Output

 

 

 

_CxFx.Reset

R/W

Bit

Set ON to reset CxFx count

_CxFx.Timeout

 

 

 

_Outx.AtPosition

RO

Bit

ON when CTRIO2 has reached Target Position

_Outx.AtVelocity

 

 

 

_Outx.Direction

RO

Bit

ON when motor is moving counter-clockwise

_Outx.EnableOutput

 

 

 

_Outx.GotoPosition

R/W

Bit

Set ON to initiate a move; CTRIO2 resets OFF when moving

_Outx.Output

 

 

 

_Outx.OutputActive

RO

Bit

ON when CTRIO2 output is generating pulses

_Outx.OutputEnabled

RO

Bit

ON when E/R input comes ON which enables the CTRIO2 output

_Outx.OutputPosition

RO

Dword

CTRIO2 output raw position (or encoder feedback position if CTAXCFG is configured as such)

_Outx.OutputStalled

RO

Bit

ON if CTRIO2 output cannot generate pulses because its scantime is too high

_Outx.OutputSuspended

RO

Bit

ON when the SUS input comes ON which suspends the CTRIO2 output

_Outx.OutputVelocity

RO

Dword

Current pulses per second rate being output by the CTRIO2

_Outx.TableComplete

 

 

 

.ErrorCode

RO

Word

Last CTRIO2 error code

.Mode

RO

Word

Indicates CTRIO2 mode: 2 = RUN; 1 = PROGRAM

.ScanTime

RO

Word

CTRIO2 scantime in microseconds

.MaxScanTime

RO

Word

Maximum CTRIO2 scantime in microseconds

.InputState

RO

Word

Upper byte is not used. Lower byte's nibbles indicate CTRIO2's channel's input's state in order: .ChxD, .ChxC, .ChxB, .ChxA. It is a composite of these members

.OutputState

RO

Word

Each nibble indicates a CTRIO2 output configuration and state: .OutxType, .OutxDiscOn, .OutxDiscEnabled, .OutxPulseActive. It is a composite of these members

.ChxA

RO

Bit

ON when CTRIO2 Channel x Input A is ON

.ChxB

RO

Bit

ON when CTRIO2 Channel x Input B is ON

.ChxC

RO

Bit

ON when CTRIO2 Channel x Input C is ON

.ChxD

RO

Bit

ON when CTRIO2 Channel x Input D is ON

.OutxType

RO

Bit

Configuration: ON if CTRIO2 output x is configured for pulse output

.OutxDiscOn

RO

Bit

Status: ON if CTRIO2 output x logic is ON (if output x is enabled then the physical output will also be ON)

.OutxDiscEnabled

RO

Bit

Configuration: ON if CTRIO2 output x is configured for discrete output

.OutxPulseActive

RO

Bit

Status: ON if CTRIO2 output x is generating pulses

 


See Also:

 


Example 1 of 2:

Description of a Typical CTRIO2 Axis Configuration (CTAXCFG) Stage Diagram:

To the right is a stage diagram of a simple sequence control that would move a motor to any number of positions and stop.

 

Initially the Config stage waits for Begin to come ON. When Begin comes ON, the CTRIO2 axis is configured and the process transitions to the Position stage.

 

The Position stage puts the CTRIO2 pulse output in the Dynamic Position mode. Once this is complete (Ready = ON) then the Move stage is enabled (not transitioned to). The reason for this is because the Position stage must remain enabled to keep the CTRIO2 pulse output in the Dynamic Position mode through the whole process.

 

The Move stage sets the CTRIO2's GotoPosition bit and waits for the AtPosition bit to come on indicating the pulse output has reached its position (Positioned = ON). Then the stage transitions to the InPos stage.

 

The InPos stage waits for either the NextMove or the Done buttons. If this was the last move, then the Done button converges both the Position and InPos stage and transitions to the Stop stage. If this was not the last move, then another position is given and the NextMove button transitions back to the Move stage.

 

The Stop stage simply exits this Program code block.

 

Description of a Typical CTRIO2 Axis Configuration (CTAXCFG) Stage Ladder:

To the right is the ladder equivalent of the above stage diagram that uses the CTAXDYNP instruction which will move a stepper motor attached to the CTRIO2's pulse output to any number of subsequent positions utilizing an axis configuration (CTAXCFG) profile, and then stop. Click here for more information on the CTAXCFG instruction.

 

This example presupposes the existence of the following System Configuration for the CTRIO2 (PLC --> System Configuration --> Module Configuration(s) --> CTRIO_000 -->):

  • Configure I/O --> Outputs --> Out0 --> Pulse (Step/Dir) or Pulse (CW/CCW).

  • A stepper motor is wired to CTRIO2's Output 0 and Output 1.

 

Config is the initial stage which waits for the input Begin to come ON. It is assumed that the first position value is loaded into the Target variable before turning on the Begin bit. Once Begin comes ON the PositionEnable bit is set ON, the CTAXCFG instruction configures an axis and when it is finished it jumps to the Position stage.

 

Position is the main CTAXDYNP instruction stage. This stage remains enabled during all moves. Instead of transitioning to the next stage (Move), the next stage will merely be enabled. PositionEnable is already ON when first entering this stage and will enable the CTAXDYNP instruction. Then the following things occur:

  1. The Pulse Output Device ($CTRIO_000_Out0) will be placed in the "Dynamic Position Mode."

  2. The current position value ($CTRIO_000_Out0.OutputPosition) is set to 0 because the Current Position parameter is set to "Zero-out".

  3. The CTRIO2's Pulse Output is enabled ($CTRIO_000_Out0.OutputEnabled = ON).

 

The PositionEnable bit will remain ON for all moves. It will be cleared OFF at the completion of the last move.

 

The CTAXDYNP's SUS (Suspend) input is controlled by the Suspend bit. This bit must remain OFF for any given move to complete. Turning this bit ON will cause the CTRIO2's output to decelerate and stop. Turning it back OFF will cause the CTRIO2's output to accelerate and complete a move.

 

The On Success parameter jumps to the Stop stage. This will occur when PositionEnable is cleared OFF and everything was successful.

 

The On Error parameter jumps to the ErrorStage stage. In this stage should exist logic (not shown here) that would properly handle the error (e.g. to process the $CTRIO_000.ErrorCode value).

 

Once the CTAXDYNP is enabled, the $CTRIO_000_Out0.OutputEnabled bit will be set ON by the Pulse Output Device (this could take a couple of scans). When this occurs the next stage (Move) is enabled.

 

Move stage accomplishes all moves. In order to do this the newest position value is assumed to be already written to the Target and the $CTRIO_000_Out0.GotoPosition bit is set ON. The Pulse Output Device will clear this bit when the move begins. Once the bit is cleared, then the $CTRIO_000_Out0.AtPosition bit is monitored for completion of the move. Once that bit is set ON by the Pulse Output Device, this move is complete and the Move stage transitions to the InPos stage.

 

The InPos stage waits for either the NextMove or Done bit. If this was not the last move, then a new position value is written to the Target variable and the NextMove bit is toggled. This causes a transition back to the Move stage. If this was the last move, then the Done bit is toggled. This disables the InPos stage and resets the PositionEnable bit.

 

The PositionEnable bit resets the CTAXDYNP instruction in the Position stage above. This causes the following to happen:

  1. The CTRIO2 pulse output is disabled ($CTRIO_000_Out0.OutputEnabled = OFF).

  2. The On Success transitions to the Stop stage.

 

The Stop stage merely exits this Program code block.


Example 2 of 2: