News:

  • October 16, 2026, 10:47:06 PM

Login with username, password and session length

Author Topic: CTRIO (H0) and homing  (Read 19628 times)

S.Cothran

  • Newbie
  • *
  • Posts: 2
CTRIO (H0) and homing
« on: April 24, 2012, 04:28:21 PM »
I have a H0 in a Dl06, both have been updated to the latest firmware. My "home" function is the basic function listed in the manual. I use the first item.."Run to limit". If I set the limit input to 1C, the home code will not execute. If I use 1D, it works fine. By design or quirk?

Greg

  • HostTech
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 702
  • Hmmm...
    • Host Engineering, Inc.
Re: CTRIO (H0) and homing
« Reply #1 on: April 25, 2012, 10:26:09 AM »
This should work. I just tested my H2-CTRIO (didn't try H0-CTRIO, but should be the same) with this and it worked.

What value are you writing to Parameter2?

For instance, I configured Out0/Out1 as pulse output. And configured Ch1/InputC and Ch1/InputD both as Limit0.

Then I ran Run-to-Limit with Parameter2 = 0x0000 (use Ch1/InC HIGH as limit). Works.
Then I ran Run-to-Limit with Parameter2 = 0x0100 (use Ch1/InD HIGH as limit). Works.
There are two types of people in the world; those that can extrapolate from incomplete data sets.

S.Cothran

  • Newbie
  • *
  • Posts: 2
Re: CTRIO (H0) and homing
« Reply #2 on: May 21, 2012, 10:36:10 AM »
My bad...thanks. I suppose I (wrongly) assumed setting the function on the home screen configured the input also, Sorry to waste your time.