News:

  • November 28, 2026, 10:22:04 PM

Login with username, password and session length

Author Topic: DM2 CPU?  (Read 74602 times)

Scooter

  • Jr. Member
  • **
  • Posts: 14
Re: DM2 CPU?
« Reply #15 on: July 23, 2026, 11:48:04 AM »
It sure would be nice to be able to connect USB devices into the BRX. One thing I always wished that I could connect was a USB based barcode reader. I'm assuming that there must be some good reason why you guys never developed this capability.

There seems to be a limit of 1024 bytes associated with various "processes", STREAMIN comes to mind as one example. You can only download 1024 bytes each time that instruction is run. STRPRINT might be another example. Are you giving any thought to increasing the size to any of these?

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: DM2 CPU?
« Reply #16 on: July 23, 2026, 03:42:03 PM »
It sure would be nice to be able to connect USB devices into the BRX. One thing I always wished that I could connect was a USB based barcode reader. I'm assuming that there must be some good reason why you guys never developed this capability.

There seems to be a limit of 1024 bytes associated with various "processes", STREAMIN comes to mind as one example. You can only download 1024 bytes each time that instruction is run. STRPRINT might be another example. Are you giving any thought to increasing the size to any of these?

USB mastering requires different hardware and lots of driver support. It isn't trivial if you don't have a OS. We choose not to have an OS to reduce the hack risk.

The 1024 limit is internal buffering. That would be be easy to increase with our next hardware.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

brucek

  • Sr. Member
  • ****
  • Posts: 62
Re: DM2 CPU?
« Reply #17 on: July 27, 2026, 07:01:10 AM »
Is there any way to add more Remote I/O? the 16 limit seems low. If you use some edrv100's you lose out pretty fast.

Controls Guy

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 3628
  • Darth Ladder
Re: DM2 CPU?
« Reply #18 on: July 27, 2026, 01:23:03 PM »
Is there any way to add more Remote I/O? the 16 limit seems low. If you use some edrv100's you lose out pretty fast.

Use Modbus instead of native?   Not sure if the Modbus scanner is limited to 16 server/slaves, but I doubt if MRX/MWX is.
I retract my earlier statement that half of all politicians are crooks.  Half of all politicians are NOT crooks.  There.

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: DM2 CPU?
« Reply #19 on: July 28, 2026, 10:05:51 AM »
The DM2 will have more processor power and much more memory, so yes, we could easily increase capacities like this. It's always a balance between expected use cases and available resources.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

LennyG

  • Newbie
  • *
  • Posts: 8
Re: DM2 CPU?
« Reply #20 on: August 02, 2026, 12:33:48 PM »
EtherCAT support. A lot more items are moving to that from RS-485 and jumping over modbus TCP. Would be nice of the support from a POM or a secondary Ethernet port.

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: DM2 CPU?
« Reply #21 on: August 03, 2026, 12:27:34 PM »
EtherCAT support. A lot more items are moving to that from RS-485 and jumping over modbus TCP. Would be nice of the support from a POM or a secondary Ethernet port.

It's been discussed. POM probably is too limited, but a module would be fine. Biggest question is exactly what people would want supported.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

Kristjan

  • Sr. Member
  • ****
  • Posts: 90
    • Idnadartaekni ehf
Re: DM2 CPU?
« Reply #22 on: August 11, 2026, 07:00:50 AM »
How about a more powerful webserver? One that makes it easier to create dynamic HTML pages. A few use cases I would find useful:
  • Create pages for I/O testing: show status of digital and analog inputs and allow toggling of digital outputs and writing analog outputs. This would enable early on-site testing by the electrical contractor.
  • Programmatically generate a page of current Modbus registers, showing Modbus address, Nickname, Extra Info, Description. Add an export button for the list. The list on the page would be created when the page is called and be populated with the actual valid register list. This would allow a 3rd party system integrator to read the actual valid Modbus register list.
  • Create a simple user interface for operators. Showing process variables, setpoints etc. This would be a useful operator interface, served directly from the PLC itself.
« Last Edit: August 12, 2026, 04:54:20 PM by Kristjan »

LennyG

  • Newbie
  • *
  • Posts: 8
Re: DM2 CPU?
« Reply #23 on: August 31, 2026, 04:58:48 PM »
EtherCat Support

LennyG

  • Newbie
  • *
  • Posts: 8
Re: DM2 CPU?
« Reply #24 on: October 24, 2026, 10:49:09 PM »
Better support for EDS files for ether net IP would be nice. All the EDS I have tried loading have failed on the BRX because they exceed the size limits.
Also, EtherCAT Support

Kristjan

  • Sr. Member
  • ****
  • Posts: 90
    • Idnadartaekni ehf
Re: DM2 CPU?
« Reply #25 on: October 31, 2026, 08:38:26 AM »
Command Line Interface (CLI) for DoMore Designer could give AI-tools handles to configure, program, test and troubleshoot.

A subset of the above is AI supported PID Autotune. I was struggling with a loop the other day and sent a screenshot of the PID view with wild fluctuations to Gemini and got very helpful guidance.

plcnut

  • Hero Member
  • *****
  • Posts: 816
    • premiersi.com
Re: DM2 CPU?
« Reply #26 on: November 04, 2026, 03:53:31 PM »
Command Line Interface (CLI) for DoMore Designer could give AI-tools handles to configure, program, test and troubleshoot.

A subset of the above is AI supported PID Autotune. I was struggling with a loop the other day and sent a screenshot of the PID view with wild fluctuations to Gemini and got very helpful guidance.
What seems to be even better is if the project were stored as xml or some other file type that can actually be read.
Version control is highly important for me, and so for now I have to rely on doing a program export so I can track changes (LLM's can use the export to give feedback as well).
Circumstances don't determine who we are, they only reveal it.

~Jason Wolthuis
Premier Systems Integration, LLC
https://premiersi.com