I have a BRX in operation, and due to supply issues, need to swap an output module from Sourcing to Sinking (BX-16TD2 -> BX-16-TD1) and of course the downstream components.  Can this swap be done by powering down, switching modules, and powering back up?  Or does it need to be powered up in PRG mode, and the program changed to reflect the new module?

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: Swapping from Sourcing to Sinking Output Module
« Reply #1 on: February 21, 2022, 11:12:36 AM »
I have a BRX in operation, and due to supply issues, need to swap an output module from Sourcing to Sinking (BX-16TD2 -> BX-16-TD1) and of course the downstream components.  Can this swap be done by powering down, switching modules, and powering back up?  Or does it need to be powered up in PRG mode, and the program changed to reflect the new module?

If it is Auto I/O config, and if memory serves, it will drop into STOP mode when it sees the change. Just need to use the switch to go back to RUN.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

Bolt

  • Hero Member
  • *****
  • Posts: 598
Re: Swapping from Sourcing to Sinking Output Module
« Reply #2 on: February 21, 2022, 11:32:50 AM »
If your memory serves, or the PLC's memory serves? ;D

Thanks, I did have it in manual config still, so have updated the PLC to auto config.

Hopefully I can just ship the parts to the onsite electrician and have him do the swap, saving me a trip to the site, or a hasty log in when he discovers it's not working.

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: Swapping from Sourcing to Sinking Output Module
« Reply #3 on: February 21, 2022, 01:15:33 PM »
If your memory serves, or the PLC's memory serves? ;D

Thanks, I did have it in manual config still, so have updated the PLC to auto config.

Hopefully I can just ship the parts to the onsite electrician and have him do the swap, saving me a trip to the site, or a hasty log in when he discovers it's not working.

Definitely mine.  ;)

In Auto it should be fine. With manual it will definitely complain.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO