« on: November 15, 2021, 12:47:43 PM »
Are the statistics for the Ethernet IO monitor calculated in DMD or the PLC? Occasionally while I am watching the monitor the packets per second will drop to zero. If in DMD I assume that this has to do with latency. If in the PLC then I think that I have a problem.

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: ETHERNET IO Monitor
« Reply #1 on: November 15, 2021, 09:00:44 PM »
Are the statistics for the Ethernet IO monitor calculated in DMD or the PLC? Occasionally while I am watching the monitor the packets per second will drop to zero. If in DMD I assume that this has to do with latency. If in the PLC then I think that I have a problem.

The update rate is DmD side. If you aren't seeing timeouts or retries in the status, the PLC side is fine.