News:

  • November 23, 2026, 12:06:22 PM

Login with username, password and session length

Author Topic: ETHERNET IO Monitor  (Read 6309 times)

mhw

  • Hero Member
  • *****
  • Posts: 250
ETHERNET IO Monitor
« on: November 15, 2021, 12:47:43 PM »
Are the statistics for the Ethernet IO monitor calculated in DMD or the PLC? Occasionally while I am watching the monitor the packets per second will drop to zero. If in DMD I assume that this has to do with latency. If in the PLC then I think that I have a problem.

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: ETHERNET IO Monitor
« Reply #1 on: November 15, 2021, 09:00:44 PM »
Are the statistics for the Ethernet IO monitor calculated in DMD or the PLC? Occasionally while I am watching the monitor the packets per second will drop to zero. If in DMD I assume that this has to do with latency. If in the PLC then I think that I have a problem.

The update rate is DmD side. If you aren't seeing timeouts or retries in the status, the PLC side is fine.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO