Well,
To get you started, I installed the beta EBC firmware that you sent (referencing the system shown in ModuleError.png that I uploaded). After updating, it cleared the error in the I/O system window that I had been seeing associated with the 08UT. Then it brought up errors for the next module, the 8 channel 8AD on channels 7 and 8. When I set up the AD I only had 6 of the channels hooked up to sensors. Channels 7 and 8 I believe are currently open. It was reporting channels 7 and 8 being out of range as they were left set-up to the (I believe) default of 4-20 mA. I went in and changed these channels from 4-20 mA to +- 10V and these errors went away. This got me to thinking, why is there no option to disable AD channels like there is for 08UT channels? It appears that part of the problem that I was seeing had to do with incorrect reporting of errors that were on a different module. Does this make sense based on the changes you made?
*Edit: The error reported was Channel Failure, not Out of Range on the AD module.