News:

  • November 22, 2026, 08:00:56 AM

Login with username, password and session length

Author Topic: Connection Status to Modbus Device  (Read 6296 times)

RBPLC

  • Hero Member
  • *****
  • Posts: 586
Connection Status to Modbus Device
« on: November 11, 2020, 08:16:17 PM »
Is there a structure associated with a created device that can be used for connection status monitoring? For example, if I've created a Modbus TCP device is there a status indicator bit that tells me I have good comms with the device?

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: Connection Status to Modbus Device
« Reply #1 on: November 12, 2020, 01:24:24 AM »
Is there a structure associated with a created device that can be used for connection status monitoring? For example, if I've created a Modbus TCP device is there a status indicator bit that tells me I have good comms with the device?

Not for clients, only servers. If I?m trying to get error rates, I just use the error bit from the instruction to drive an INC instruction.

We are beginning work shortly on a new Modbus device-centric scanner function that will have an associated structure and health status. It?ll be in 3.0 next year.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO