Scenario:
BX-08AD-3 Module attached at first slot on BX-DM1E-18ED23-D.
WX1 is off with WX2, WX3 and WX4 on. All analog inputs are setup such that:
Analog Input: 0-5, Enable Scaling: WX2 min = 0, WX2 max=32267, RX2 min=0, RX2 max=5. This is the same setup for WX3 and WX4. When I apply a process calibrator at 0VDC to the input I see 0 VDC +/- 0.003VDC. When I remove the process calibrator from the channel, Counts jump to about 4100 corresponding to 0.625 volts. This reading is the same when the terminal block is completely removed. What's the deal?

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: BX-08AD-3 Module Question
« Reply #1 on: October 02, 2020, 12:47:41 PM »
Scenario:
BX-08AD-3 Module attached at first slot on BX-DM1E-18ED23-D.
WX1 is off with WX2, WX3 and WX4 on. All analog inputs are setup such that:
Analog Input: 0-5, Enable Scaling: WX2 min = 0, WX2 max=32267, RX2 min=0, RX2 max=5. This is the same setup for WX3 and WX4. When I apply a process calibrator at 0VDC to the input I see 0 VDC +/- 0.003VDC. When I remove the process calibrator from the channel, Counts jump to about 4100 corresponding to 0.625 volts. This reading is the same when the terminal block is completely removed. What's the deal?

Are they disconnected? Voltage inputs are pretty high impedance and can float when disconnected.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

RBPLC

  • Hero Member
  • *****
  • Posts: 586
Re: BX-08AD-3 Module Question
« Reply #2 on: October 02, 2020, 12:58:33 PM »
Yes, they're disconnected completely when the terminal block is pulled out. The issue with this is that if you've got a sensor that comes unplugged or a wire gets cut for example, these inputs appear to float which could be bad news. 

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: BX-08AD-3 Module Question
« Reply #3 on: October 02, 2020, 01:12:58 PM »
Yes, they're disconnected completely when the terminal block is pulled out. The issue with this is that if you've got a sensor that comes unplugged or a wire gets cut for example, these inputs appear to float which could be bad news.

And that is why most use 4-20ma in industrial environments. If you don't mind a small loss of accuracy, add a 100k or 1M ohm resistor to ground. That should pull it to ground without disturbing the result.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

RBPLC

  • Hero Member
  • *****
  • Posts: 586
Re: BX-08AD-3 Module Question
« Reply #4 on: October 02, 2020, 02:50:42 PM »
4-20 sensors aren't always an option. I'm wondering if anyone else has ran into this and if there's a better option than jumping a resistor on a terminal block. What's the feasibility of adding a pull-down to the module?