Scenario:
BX-08AD-3 Module attached at first slot on BX-DM1E-18ED23-D.
WX1 is off with WX2, WX3 and WX4 on. All analog inputs are setup such that:
Analog Input: 0-5, Enable Scaling: WX2 min = 0, WX2 max=32267, RX2 min=0, RX2 max=5. This is the same setup for WX3 and WX4. When I apply a process calibrator at 0VDC to the input I see 0 VDC +/- 0.003VDC. When I remove the process calibrator from the channel, Counts jump to about 4100 corresponding to 0.625 volts. This reading is the same when the terminal block is completely removed. What's the deal?