Performance observations:

Gmail seems to timeout after 9-10 seconds if the email is not sent successfully (thus the 12 second timeout in the Do-More SMTP config)

The transaction seems to take 1.85-1.90s of CPU time regardless of time slice (CPU fraction dedicated to the EMAIL).    Total CPU time is very consistent across a range of CPU fraction from just over 20% to 65% which was the highest we tested, so it looks like the process is bound by the Do-More and there's no time spent waiting on Gmail at these transaction times.  Internet bandwidth shouldn't be critical If we're Do-More bound for speed, but while I was testing this I had 10.8 Mbps down, 2.2 up.

The EMAIL needs a minimum of 21% of CPU time in order to allocate 1.90s of CPU time before the Gmail timeout, so for a 1666us TLS time slice, the average scan time while not emailing needs to be under 6.2ms.
I retract my earlier statement that half of all politicians are crooks.  Half of all politicians are NOT crooks.  There.

steve66

  • Newbie
  • *
  • Posts: 4
Re: Help with EMAIL
« Reply #16 on: November 17, 2020, 10:10:50 PM »
Are there any plans for a future update for the Do More to get the SSL authentication like the BRX PLCs have?

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: Help with EMAIL
« Reply #17 on: November 17, 2020, 11:40:42 PM »
Are there any plans for a future update for the Do More to get the SSL authentication like the BRX PLCs have?

While possible, it isn?t easy for some really dumb reasons, so probably not.