News:

  • November 22, 2026, 07:20:40 AM

Login with username, password and session length

Author Topic: Help with EMAIL  (Read 25672 times)

Controls Guy

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 3628
  • Darth Ladder
Re: Help with EMAIL
« Reply #15 on: September 09, 2020, 07:10:09 PM »
Performance observations:

Gmail seems to timeout after 9-10 seconds if the email is not sent successfully (thus the 12 second timeout in the Do-More SMTP config)

The transaction seems to take 1.85-1.90s of CPU time regardless of time slice (CPU fraction dedicated to the EMAIL).    Total CPU time is very consistent across a range of CPU fraction from just over 20% to 65% which was the highest we tested, so it looks like the process is bound by the Do-More and there's no time spent waiting on Gmail at these transaction times.  Internet bandwidth shouldn't be critical If we're Do-More bound for speed, but while I was testing this I had 10.8 Mbps down, 2.2 up.

The EMAIL needs a minimum of 21% of CPU time in order to allocate 1.90s of CPU time before the Gmail timeout, so for a 1666us TLS time slice, the average scan time while not emailing needs to be under 6.2ms.
I retract my earlier statement that half of all politicians are crooks.  Half of all politicians are NOT crooks.  There.

steve66

  • Newbie
  • *
  • Posts: 4
Re: Help with EMAIL
« Reply #16 on: November 17, 2020, 10:10:50 PM »
Are there any plans for a future update for the Do More to get the SSL authentication like the BRX PLCs have?

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: Help with EMAIL
« Reply #17 on: November 17, 2020, 11:40:42 PM »
Are there any plans for a future update for the Do More to get the SSL authentication like the BRX PLCs have?

While possible, it isn?t easy for some really dumb reasons, so probably not.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO