News:

  • October 10, 2026, 03:35:29 PM

Login with username, password and session length

Author Topic: Do More  (Read 7281 times)

Henryp

  • Hero Member
  • *****
  • Posts: 161
Do More
« on: December 16, 2019, 03:15:42 PM »
Should a DM PLC with the term switch set to run mode allow the ladder to be edited?

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3848
    • Host Engineering
Re: Do More
« Reply #1 on: December 16, 2019, 03:25:35 PM »
Yes.  Do-more supports Run Time Edit.

If you are wanting some kind of "write project" protection - look at the User/Password capability of Do-more.  The default (no password) default is read/write data, read/write program.  You can change the Default to be read/write data, read program (not read/write program).  Designer will still let you "edit" the program and save it to disk, but it would not let you (as the Default user) to write the program.

Is this the kind of functionality you are wanting?

Henryp

  • Hero Member
  • *****
  • Posts: 161
Re: Do More
« Reply #2 on: December 16, 2019, 06:35:47 PM »
I'm looking for what I believe the DL PLCs do when the terminal switch is in run mode, no online edits only when it is terminal mode.
« Last Edit: December 17, 2019, 06:40:42 PM by Henryp »

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6176
  • Yes Pinky, Do-more will control the world!
Re: Do More
« Reply #3 on: December 16, 2019, 08:27:25 PM »
I'm looking for what I believe the a DL PLCs when the terminal switch is in run mode no online edits only when it is terminal mode.

The switch on Do-more only governs mode changes, not program updates, but there are multiple ways to prevent program updates on Do-more. Setting ST21 to true will do so. You could use an X input to control it. You can also restrict various login permissions to limit who has write access to the program.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO