When doing peerlink via the ECOM100 module in a Do-more PLC, the peerlink is using DL legacy addressing. So instead of PL, use DLV block in both PLCs. Note that DLV block uses octal addressing since that is the legacy addressing of V memory in DirectLogic PLCs. So the first block, based on your configuration, will show up in DLV0 through DLV17