I have 14 Yaskawa v1000 drives that I want to use explicit Ethernet messaging to operate. We are using a DoMore BRX cpu. I have bench tested one drive it works fine I can send/ receive all of the information. I am messaging using assemblies 21/71. I am connected to the network the MS light is solid green but the NS light is flashing green, All works but on any other system I use the NS light is solid green when it is on the system and working with the PLC. I called Yaskawa Tech support and they said the SI-EN3/V module may be defective However I tried two new one and the same result. I know there are some of you guys that have used Yaskawa drives (which we really like) and the DoMore (which we also like) to talk Ethernet I/P is it normal for the NS light not to be solid green, or do I have a problem. We have install thousands of the Yaskawa drives on Rockwell, GE, Modicon, etc. but this is the first DoMore with Ethernet.

Thanks for any help or insight you can give. I don't want the customer to have a problems with this setup, we talked them into the DoMore away from Rockwell and if it go well we hope to keep using DoMore in their factory.

JW
« Last Edit: May 26, 2019, 12:10:47 PM by jwbaker3 »

Mike Nash

  • Hero Member
  • *****
  • Posts: 655
Re: DoMore to Yaskawa v1000 ethernet
« Reply #1 on: May 26, 2019, 01:56:32 PM »
Unfortunately, while I have done it with the D-more H2 and BRX, with the V1000, A1000 and GA800, at least bench testing, I don't recall paying attention to the NS LED.

I do know that the Yaskawa EIP may not detect a coms loss due to the PLC not talking or loss of Ethernet by pulling the cable anywhere other than switch to drive. I suspect this is due to explicit messages not leaving a connection open. I don't think I saw this with Modbus TCP. Implicit messaging doesn't have an issue either.

I recently did a Toshiba AS3 with AB and noticed it has a timeout parameter that can be set to monitor for lack of activity.

Then again, it's the weekend and I could be mis-remembering some of this.

Controls Guy

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 3628
  • Darth Ladder
Re: DoMore to Yaskawa v1000 ethernet
« Reply #2 on: May 26, 2019, 07:52:11 PM »
Maybe it's lighting up for active polling and the other PLC's are polling more rapidly than the BRX.  Or maybe it indicates an open connection and the BRX is opening/comming/closing each time where the others keep it open?  Maybe check the Yaskawa docs to see what the LED represents.  Haven't done a whole lot of EIP except for AB <-> AB and tests with BRX, so don't really remember the protocol specifics.
I retract my earlier statement that half of all politicians are crooks.  Half of all politicians are NOT crooks.  There.

jwbaker3

  • Hero Member
  • *****
  • Posts: 144
Re: DoMore to Yaskawa v1000 ethernet
« Reply #3 on: June 03, 2019, 09:21:39 AM »
Thanks guys, I think you are correct its the explicit messaging not keep a connection with the drive. The NS light flashing green per the manual is (Operating Status) = "Online communications not established" (Remarks) = "The option is on line without an established connection" The tech support guy was surprised it was working so I sent him a video. 