News:

  • October 23, 2026, 12:19:46 PM

Login with username, password and session length

Author Topic: BX-P-ECOMLT and Modbus TCP  (Read 7776 times)

mfloresh

  • Newbie
  • *
  • Posts: 8
BX-P-ECOMLT and Modbus TCP
« on: February 01, 2018, 08:27:11 PM »
Hello,

I have read in some of the posts that the BX-P-ECOMLT has certain limitations. I am trying to use it as a Modbus TCP server, but I cannot get it to work.  The main Ethernet port works just fine but not the ECOMLT port. According to the BRX manual, it says it supports Modbus TCP server, but I did not find an option to enable the Modbus TCP server for the ECOMLT anywhere, just an option to enable it in the main port.

Any thoughts?

Thanks,

Miguel

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6177
  • Yes Pinky, Do-more will control the world!
Re: BX-P-ECOMLT and Modbus TCP
« Reply #1 on: February 01, 2018, 09:15:07 PM »
The initial firmware release didn't support it, it was added after launch, so make sure you're up to date. No configuration is required in DmD, it just works.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

mfloresh

  • Newbie
  • *
  • Posts: 8
Re: BX-P-ECOMLT and Modbus TCP
« Reply #2 on: February 01, 2018, 11:21:42 PM »
Thanks for the prompt reply. I was not aware that the firmware in BX-P-ECOMLT is upgradeable with NetEdit. I will give this a shot.

Regards,

Miguel

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6177
  • Yes Pinky, Do-more will control the world!
Re: BX-P-ECOMLT and Modbus TCP
« Reply #3 on: February 02, 2018, 12:00:10 AM »
Thanks for the prompt reply. I was not aware that the firmware in BX-P-ECOMLT is upgradeable with NetEdit. I will give this a shot.

Regards,

Miguel


Yes, it is. Let us know if that fixes it for you.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO