News:

  • October 18, 2026, 06:34:24 AM

Login with username, password and session length

Author Topic: Disabling specific automatic reads from ethernet side of gateway  (Read 51733 times)

stoic-one

  • Full Member
  • ***
  • Posts: 36
Is this possible?

Edit:
The reason I'm asking is because the RTU side bogs down pretty badly when a node drops off or is disabled when auto reads are enabled...
« Last Edit: July 19, 2015, 01:02:29 PM by stoic-one »

MikeS

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 270
    • Host Engineering, Inc.
Re: Disabling specific automatic reads from ethernet side of gateway
« Reply #1 on: July 20, 2015, 04:30:41 PM »
there's current;y no way to get the gateway to stop trying to process all of the automatic reads.

you may want to try reducing the timeouts to as low a value as is reasonable and setting the retries to 0, to get the nodes that are offline to fail as quickly as possible, thus letting the functioning nodes update as quickly as possible.
Good design costs a lot. Bad design costs even more.

stoic-one

  • Full Member
  • ***
  • Posts: 36
Re: Disabling specific automatic reads from ethernet side of gateway
« Reply #2 on: July 20, 2015, 07:22:58 PM »
What effect does that have when they come back online?

MikeS

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 270
    • Host Engineering, Inc.
Re: Disabling specific automatic reads from ethernet side of gateway
« Reply #3 on: July 21, 2015, 10:16:09 AM »
when they come back online the comm should just pick up and work. each entry in the list of automatic reads is an autonomous operation.
Good design costs a lot. Bad design costs even more.