News:

  • November 27, 2026, 12:52:08 AM

Login with username, password and session length

Author Topic: Capturing pulses  (Read 7992 times)

Garyhlucas

  • Hero Member
  • *****
  • Posts: 421
Capturing pulses
« on: April 24, 2015, 09:29:47 PM »
I want to try capturing pulses from a flow meter using a regular digital input.  I don't believe the rate is terribly high, maybe 100 hertz. Is this doable or will I need a high speed counter module?  The reason for doing this is to keep the cost down on the system I am designing.  I don't need high accuracy, a missed pulse here and there would not be an issue.  How should I code this?

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: Capturing pulses
« Reply #1 on: April 25, 2015, 12:26:10 AM »
You're on the edge. A Do-more controller can keep up, but your DC input is iffy. For 100hz you need better than 5ms response on the input.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO