Author Topic: Field I/O RTD input Module  (Read 3516 times)

duvals

  • Newbie
  • *
  • Posts: 4
Field I/O RTD input Module
« on: August 22, 2012, 03:37:36 PM »
I'm unable to configure the module. My setup is:
Main PLC D2-260 with module H2-ERM

Slave: T1H-EBC100, T1F-16RTD.

I use the ERM Workbench to configure the module with the default configuration and mapping.

I use the latest firmware in all module.

Does someone have already use this config???

Greg

  • HostTech
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 668
  • Why for you bury me in the cold, cold ground?
    • Host Engineering, Inc.
Re: Field I/O RTD input Module
« Reply #1 on: August 22, 2012, 04:35:51 PM »
What setup are you wanting to do? The RTD types are set by jumpers on the T1F-16RTD module.
Input word 1-2 = Ch1
Input word 3-4 = Ch2
.
.
.
Input word 29-30 = Ch15
Input word 31-32 = Ch16

Or do you mean ERM Workbench gets an error when trying to write the configuration to the ERM? If so, what is the error?
« Last Edit: August 22, 2012, 04:40:09 PM by Greg »
There are two types of people in the world; those that can extrapolate from incomplete data sets.