News:

  • October 17, 2026, 06:10:25 AM

Login with username, password and session length

Author Topic: Use of encoder input signals H2-CTRIO  (Read 17832 times)

eric14779

  • Full Member
  • ***
  • Posts: 30
Use of encoder input signals H2-CTRIO
« on: May 02, 2012, 10:57:21 AM »
I have encoder signals

A
A'not'

B
B'not'

Z
Z'not'

the encoder wiring diagram shows using overall shield and twisted pairs for the signal & signal'not'  for each A,B,& Z

the CTRIO wiring shows using only the  A, B, & Z signals with a common.

I had done a encoder project a couple of years ago and I do not remember what i did with the 3 'not' signals at the CTRIO or if i just did not use them.

And if I do not use them should I use shielded wire and not have any twisted pairs or at least keep the A, B, & Z signals in separate pairs.

Thanks,

b_carlton

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 606
    • thePLCguy
Re: Use of encoder input signals H2-CTRIO
« Reply #1 on: May 02, 2012, 11:09:03 AM »
Verify that your 'A' etc signals meet the 9-30 VDC requirement for counter inputs. I suspect that they may only be 5 volts.
An output is a PLC's way of getting its inputs to change.

eric14779

  • Full Member
  • ***
  • Posts: 30
Re: Use of encoder input signals H2-CTRIO
« Reply #2 on: May 02, 2012, 12:10:43 PM »
b_carlton

you are correct my signals are 5V....  ??? >:(

what do I need to do to boost the voltage....  is there a commercial device available ?

b_carlton

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 606
    • thePLCguy
Re: Use of encoder input signals H2-CTRIO
« Reply #3 on: May 02, 2012, 12:24:42 PM »
We have used http://www.bei-industrial-products.com/e_optical-isolator.html.
They aren't cheap but they are designed to specifically do this job.
An output is a PLC's way of getting its inputs to change.

eric14779

  • Full Member
  • ***
  • Posts: 30
Re: Use of encoder input signals H2-CTRIO
« Reply #4 on: May 02, 2012, 01:05:49 PM »
OK Got one on order...

Now what to do with the differential signals ??

drop them before the isolator or after ??

b_carlton

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 606
    • thePLCguy
Re: Use of encoder input signals H2-CTRIO
« Reply #5 on: May 02, 2012, 01:28:27 PM »
The input side takes the differential signals directly. After optoisolation the single-ended signals are generated and sent to the CTRIO. The diagrams are fairly specific. Diagram 1 in the specifications PDF shows exactly your setup. You'll use just the A, B and Z signals of the output on the right side. The 'Nots' on the output will be left unconnected.
« Last Edit: May 02, 2012, 01:31:55 PM by b_carlton »
An output is a PLC's way of getting its inputs to change.

eric14779

  • Full Member
  • ***
  • Posts: 30
Re: Use of encoder input signals H2-CTRIO
« Reply #6 on: May 02, 2012, 03:06:09 PM »
GREAT !!

 Thanks  b-carlton