« on: May 13, 2010, 08:17:00 PM »
I have a H2-ERM and a T1H-EBC. I want to use the EBC serial port as a MODBUS master. Is this possible? If not, then what options do I have?
« Last Edit: May 14, 2010, 07:33:26 AM by mhw »

Controls Guy

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 3628
  • Darth Ladder
Re: T1H-EBC(100) Modbus
« Reply #1 on: May 13, 2010, 08:21:04 PM »
I'm pretty sure you have the option to not do that.
I retract my earlier statement that half of all politicians are crooks.  Half of all politicians are NOT crooks.  There.

mhw

  • Hero Member
  • *****
  • Posts: 250
Re: T1H-EBC(100) Modbus
« Reply #2 on: May 13, 2010, 08:30:12 PM »
How do I identify that port in my ladder logic?

MikeS

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 270
    • Host Engineering, Inc.
Re: T1H-EBC(100) Modbus
« Reply #3 on: May 14, 2010, 08:31:02 AM »
the serial port on the T1H-EBC100 is not accessible through the ERM.
Good design costs a lot. Bad design costs even more.

mhw

  • Hero Member
  • *****
  • Posts: 250
Re: T1H-EBC(100) Modbus
« Reply #4 on: May 14, 2010, 01:57:08 PM »
What if I change the remote IO to a 205 base with a H2-EBC. Can the serial port on it serve as a MODBUS master? If yes how do I identify the port in ladder?

Greg

  • HostTech
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 702
  • Hmmm...
    • Host Engineering, Inc.
Re: T1H-EBC(100) Modbus
« Reply #5 on: May 18, 2010, 10:49:48 AM »
The serial port on none of the EBC100s is accessible through the ERM.
There are two types of people in the world; those that can extrapolate from incomplete data sets.

b_carlton

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 606
    • thePLCguy
Re: T1H-EBC(100) Modbus
« Reply #6 on: May 18, 2010, 10:54:48 AM »
MHW - this might go faster if you state exactly what equipment you have with current port usage then describe what you are trying to accomplish.
An output is a PLC's way of getting its inputs to change.

mhw

  • Hero Member
  • *****
  • Posts: 250
Re: T1H-EBC(100) Modbus
« Reply #7 on: May 18, 2010, 12:11:26 PM »
I have a 205 rack with a 260CPU, discrete IO, an ECOM for HMI, and a ERM. The ERM network consists of a couple of T1H-EBCs one with a CITRO module and the other with some discrete IO. At the discrete location there will be a third party device that can comunicate via MODBUS RTU. I was wanting to use exsiting cabling to talk to this device.

Controls Guy

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 3628
  • Darth Ladder
Re: T1H-EBC(100) Modbus
« Reply #8 on: May 18, 2010, 07:45:54 PM »
Like I said, I'm pretty sure you have the option to not do that.
I retract my earlier statement that half of all politicians are crooks.  Half of all politicians are NOT crooks.  There.

b_carlton

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 606
    • thePLCguy
Re: T1H-EBC(100) Modbus
« Reply #9 on: May 18, 2010, 11:01:32 PM »
Yes - probably extra cabling or some means of communication with the remote site is called for. Sorry.