News:

  • October 14, 2026, 10:40:54 AM

Login with username, password and session length

Author Topic: DL06 locking up  (Read 47884 times)

Controls Guy

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 3626
  • Darth Ladder
Re: DL06 locking up
« Reply #15 on: May 12, 2010, 06:55:39 PM »
Glad you noticed that Darth.  I rather hoped someone would notice my wit  :)


LBL K666
GOTO K666

PLC Program of the Beast
I retract my earlier statement that half of all politicians are crooks.  Half of all politicians are NOT crooks.  There.

WRT

  • Full Member
  • ***
  • Posts: 26
Re: DL06 locking up
« Reply #16 on: May 12, 2010, 08:00:33 PM »
This is more fun than Facebook!

b_carlton

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 606
    • thePLCguy
Re: DL06 locking up
« Reply #17 on: May 12, 2010, 09:11:43 PM »
'Farmville' on a PLC?
An output is a PLC's way of getting its inputs to change.

WRT

  • Full Member
  • ***
  • Posts: 26
Re: DL06 locking up
« Reply #18 on: May 13, 2010, 09:35:32 PM »
I finally found the lock out problem after a week of remote troubleshooting.  A Solid State relay "coil" connected to one of the PLC outputs was shorted.  I thought I was clever putting in a 1 amp power supply so that all the circuits were protected, but what happened is that the low voltage from the short killed the PLC and left it in a bad state.  No wonder it was not communicating!  I couldn't forensic it because the PLC wasn't talking every time it tried to turn that output on!

So another moral:

Put a power supply in that is hefty enough to open a separate fuse on the output circuits without dropping the voltage so much that the PLC goes down.  Even better, annunciate the fuse so you know what the problem is.

Controls Guy

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 3626
  • Darth Ladder
Re: DL06 locking up
« Reply #19 on: May 27, 2010, 02:15:22 PM »
I agree.  I usually have a dedicated fuse or breaker on the output common.  When you send your kids (wires) out in the world, you never know what's going to happen to them.   ;)
I retract my earlier statement that half of all politicians are crooks.  Half of all politicians are NOT crooks.  There.