News:

  • October 14, 2026, 12:42:16 AM

Login with username, password and session length

Author Topic: Revision History  (Read 60962 times)

MKL

  • Full Member
  • ***
  • Posts: 42
Revision History
« on: June 11, 2007, 04:34:46 PM »
hi,

on the website there's a new firmware available for the h0-ecom100: version 4.0.173

but what's new in this version? because the revision history is only to 4.0.169


MikeS

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 270
    • Host Engineering, Inc.
Re: Revision History
« Reply #1 on: June 12, 2007, 10:19:29 AM »
we're trying to fix this now, we're having some firewall difficulties with our web publishing software. in the mean time, here's the revision history for this ecom100 firmware release:

  • Added 'ECOM Advanced Settings' page to the Web browser configuration page. In previous firmware versions you could only adjust these settings via NetEdit3.
  • Fixed a problem with the Web browser configuration page where sometimes only a portion of the page would show up in the Web browser.
  • Added favicons to the Web browser configuration page.
  • If the ECOM100 receives a Modbus/TCP request for a value that is at either endpoint of the PLC's memory mapped ranges, the ECOM100 would erroneously report the value was out of range.
  • If the ECOM100 is operating as a Modbus/TCP server, the ECOM100 would not report the correct error value for a watchdog timeout error from one of it's clients.



Good design costs a lot. Bad design costs even more.

MKL

  • Full Member
  • ***
  • Posts: 42
Re: Revision History
« Reply #2 on: June 12, 2007, 12:26:50 PM »
ok thnx for the info :)