News:

  • November 30, 2026, 01:27:54 AM

Login with username, password and session length

Author Topic: BRX dropping out of run  (Read 17153 times)

jwbaker3

  • Hero Member
  • *****
  • Posts: 144
BRX dropping out of run
« on: July 07, 2026, 12:38:23 PM »
I have a system with 4 Brx plc's and a AB 5069 networked together, the Brx will randomly drop out of run. Cycle the switch and all's good (except restarting the system) could this be due to firmware? Or ? any ideas? we are talking to 5 Fanuc robots and 21 drives and messaging information between the Brx, the AB had one of the Brx setup as remote IO
Thanks,
JW

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: BRX dropping out of run
« Reply #1 on: July 07, 2026, 12:40:58 PM »
I have a system with 4 Brx plc's and a AB 5069 networked together, the Brx will randomly drop out of run. Cycle the switch and all's good (except restarting the system) could this be due to firmware? Or ? any ideas? we are talking to 5 Fanuc robots and 21 drives and messaging information between the Brx, the AB had one of the Brx setup as remote IO
Thanks,
JW

What does the log say?
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

jwbaker3

  • Hero Member
  • *****
  • Posts: 144
Re: BRX dropping out of run
« Reply #2 on: July 07, 2026, 01:43:41 PM »
plc rebooted following hardware watchdog timeout

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: BRX dropping out of run
« Reply #3 on: July 07, 2026, 02:00:18 PM »
plc rebooted following hardware watchdog timeout

Electrically noisy environment?