News:

  • November 10, 2026, 06:41:06 PM

Login with username, password and session length

Author Topic: ECOM100 blocking the bus  (Read 64542 times)

Angelo

  • Newbie
  • *
  • Posts: 5
ECOM100 blocking the bus
« on: May 06, 2026, 10:35:20 AM »
Dear all,

I have an H4-ECOM100 module, and it appears to be causing a problem in my system. When this module is installed together with the other modules, the D4-450 CPU cannot communicate with any module on the bus. However, when I remove the H4-ECOM100 module from the bus, everything returns to normal.

Therefore, I concluded that something is wrong with the H4-ECOM100 module.

Could someone please help me?

Best regards,
Angelo

Angelo

  • Newbie
  • *
  • Posts: 5
Re: ECOM100 blocking the bus
« Reply #1 on: May 06, 2026, 12:01:06 PM »
Just removed the board to make some measurements with voltimeter.

What I´ve found:

 the IC (U13) which is a LJ245A, see photo below, there is a short between ping 13 (GND) to pin 3 (A1).

See that the U15 and U14 are also the same LJ245A

The LJ245A is the marking of Texas Intrument SN74LVC4245A. This CI is Octal Bus Transceiver and 3.3-V to 5-V Shifter
With 3-State Outputs.

Using ChatGPT I got a response like this:


"9. Definitive Test

The best method is to:

remove the IC,
test whether the bus communication returns,
or replace it directly.

Since you already work with PLCs and industrial buses:

if removing the IC causes the system to “come back to life” or restores communication,
then the IC is most likely internally locking up the bus.

This is extremely common."


Which seems to be the case as it cites  "lockin up the bus"


I will try to find the IC to purchase and then replace it.
 

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3855
    • Host Engineering
Re: ECOM100 blocking the bus
« Reply #2 on: May 06, 2026, 12:07:20 PM »
It may be a bent connector pin.  405 modules have that issue since they are rotated/levered into position and the connector sometimes doesn't line up perfectly and ends up bending pin(s).

Angelo

  • Newbie
  • *
  • Posts: 5
Re: ECOM100 blocking the bus
« Reply #3 on: May 06, 2026, 10:38:28 PM »
I have checked. All pins are perfect aligned.

The system was running fine for the last 8 years, nobody removed the ECOM100 from the bus since then. So the bent pins hypothesis  would have 0% to be the case.


I forgot to ulpload the photo.

« Last Edit: May 06, 2026, 10:46:54 PM by Angelo »

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3855
    • Host Engineering
Re: ECOM100 blocking the bus
« Reply #4 on: May 07, 2026, 07:45:44 AM »
That's an FPGA, which is not field replaceable (it must also be programmed).

Contact support at hosteng.com about RMA

Angelo

  • Newbie
  • *
  • Posts: 5
Re: ECOM100 blocking the bus
« Reply #5 on: May 07, 2026, 09:45:31 PM »
That's an FPGA, which is not field replaceable (it must also be programmed).

Contact support at hosteng.com about RMA

What ? The LJ245A ?


franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3855
    • Host Engineering
Re: ECOM100 blocking the bus
« Reply #6 on: May 08, 2026, 08:36:04 AM »
The Altera part

Angelo

  • Newbie
  • *
  • Posts: 5
Re: ECOM100 blocking the bus
« Reply #7 on: May 08, 2026, 07:39:42 PM »
Ah.... ok.

But do you think the problem is the Altera chip, even with the multimeter showing a short between pin 3 and the GND pin on the LJ245 IC?

rlp122

  • Sr. Member
  • ****
  • Posts: 92
Re: ECOM100 blocking the bus
« Reply #8 on: May 09, 2026, 06:50:01 PM »
<pushes chips into center of table>

I'm all in on it being a bent or retracted pin.  This is the most common issue with this PLC.  I wouldn't place much faith in ChaptGPT, it hallucinates a lot of stuff.

Retracted pins are very hard to spot.  I couldn't even begin to count the number that I have seen in my career.  It doesn't take much, even 0.5 mm is enough to cause it to not connect fully.  Get out a magnifying glass and look very closley.

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6179
  • Yes Pinky, Do-more will control the world!
Re: ECOM100 blocking the bus
« Reply #9 on: May 10, 2026, 03:34:16 PM »
The FPGA doesn't directly connect to the bus. All bus connections are through buffers. It is certainly possible a buffer is damaged, but 405s are notorious for bent pins.

We're happy to look at the unit.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO