News:

  • November 30, 2026, 02:31:33 AM

Login with username, password and session length

Author Topic: BRX has lost IP address  (Read 99961 times)

SceneryDriver

  • Jr. Member
  • **
  • Posts: 15
BRX has lost IP address
« on: February 06, 2026, 10:38:44 PM »
All,
I have a BX-DM1E-10ED13-D with two expansion modules: BX-08TD1 and BX-08AD-1.  PLC is running fine, but I found out today that I can no longer connect to it over Ethernet.  It was programmed in Do-More Designer 2.11.1 in December, and has been running fine. 

DMD can no longer connect to it, and can't even see it.  NetEdit3 can sort of see it, but it displays an IP address of 0.0.0.0.  Last time I connected, it had the expected IP address of 10.101.50.14.  I cannot alter the IP address in NetEdit; I get an error.  I cannot ping the PLC at its expected address. 

Weirdly, the PLC is still successfully communicating with two CM5 touchscreens, and everything is still running.  I've tried a power cycle, as well as putting the PLC in STOP, switching to RUN, and back to TERM with no effect. 

Do I need to use the onboard DIP switches to go through clearing the Ethernet settings, and give the PLC its settings again?  Complicating this is the fact that I'm supporting this system from several states away, and I'd rather not bork an otherwise operating system.  I can have an onsite tech wipe the Ethernet settings if that'll help. 

I've never seen this behavior from a BRX.  What might cause the PLC to (sort of) dump its network settings, while still talking to two CM5 touchscreens over Ethernet? 


Sincerely,

SceneryDriver

SceneryDriver

  • Jr. Member
  • **
  • Posts: 15
Re: BRX has lost IP address
« Reply #1 on: February 06, 2026, 11:04:18 PM »
A bit more info: I've tried IPConfig over the VPN connection, and IPConfig can't find the PLC.


SceneryDriver

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3858
    • Host Engineering
Re: BRX has lost IP address
« Reply #2 on: February 09, 2026, 08:13:18 AM »
Is it using DHCP or did you assign it a static IP address?

SceneryDriver

  • Jr. Member
  • **
  • Posts: 15
Re: BRX has lost IP address
« Reply #3 on: February 09, 2026, 08:47:12 AM »
The PLC was assigned a static IP address and subnet mask.


SceneryDriver

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3858
    • Host Engineering
Re: BRX has lost IP address
« Reply #4 on: February 09, 2026, 09:39:14 AM »
Does your VPN network configuration supporting pinging the remote devices?

Can you ping the PLC via command line?
Can you ping the HMI panels?
Can you remotely connect to the HMI panels using their configuration software (assuming you could do this before this 0.0.0.0 issue showed up)?

SceneryDriver

  • Jr. Member
  • **
  • Posts: 15
Re: BRX has lost IP address
« Reply #5 on: February 09, 2026, 10:06:10 AM »
Does your VPN network configuration supporting pinging the remote devices?

Can you ping the PLC via command line?
Can you ping the HMI panels?
Can you remotely connect to the HMI panels using their configuration software (assuming you could do this before this 0.0.0.0 issue showed up)?

The VPN does support pinging devices on the remote network.
I cannot ping the PLC via the command line.
I can successfully ping the HMI panels.
I can remotely connect to the CM5 panels with the C-more touchscreen software.

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3858
    • Host Engineering
Re: BRX has lost IP address
« Reply #6 on: February 09, 2026, 10:10:52 AM »
Can someone remotely connect to the PLC (Ethernet, USB, Serial) and look at the SysInfo page and report what that page reports for the IP Configuration parameters on the General Information tab?

SceneryDriver

  • Jr. Member
  • **
  • Posts: 15
Re: BRX has lost IP address
« Reply #7 on: February 09, 2026, 10:51:12 AM »
Can someone remotely connect to the PLC (Ethernet, USB, Serial) and look at the SysInfo page and report what that page reports for the IP Configuration parameters on the General Information tab?

I tried that already via Ethernet (to the PLC) on a laptop running Chrome Remote Desktop (via wifi) and DMD.  I was unable to connect to the PLC or ping it when connected locally with the laptop and Chrome Remote Desktop / DMD.  I did make sure to give the laptop's Ethernet port a static IP address in the correct subnet as it was connected directly to the PLC with only a cable (no DHCP server anywhere in the mix).

I don't have a USB POM installed in the unit, and they don't have the cable to attempt a serial connection.


SceneryDriver

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3858
    • Host Engineering
Re: BRX has lost IP address
« Reply #8 on: February 09, 2026, 12:29:36 PM »
0.0.0.0 is definitely wrong - trying to figure out the extent of the failure.

Once someone remotely is able to connect to it, the System Log may have some clues as to what happened/when.

ipconfig uses directed broadcasts - if that is not working now, not sure if "clearing" the IP configuration via dipswitches will make it work over VPN, but you can try.  Hopefully that will work - and then get a copy of the System Log.


SceneryDriver

  • Jr. Member
  • **
  • Posts: 15
Re: BRX has lost IP address
« Reply #9 on: February 09, 2026, 02:03:55 PM »
0.0.0.0 is definitely wrong - trying to figure out the extent of the failure.

Once someone remotely is able to connect to it, the System Log may have some clues as to what happened/when.

ipconfig uses directed broadcasts - if that is not working now, not sure if "clearing" the IP configuration via dipswitches will make it work over VPN, but you can try.  Hopefully that will work - and then get a copy of the System Log.

I have a tech onsite who can do a direct-connect laptop running DMD, so I'll be happy if we can get it back that way at least .  I'll walk them through clearing the IP config via the DIP switches this afternoon and report back.


SceneryDriver

SceneryDriver

  • Jr. Member
  • **
  • Posts: 15
Re: BRX has lost IP address
« Reply #10 on: February 09, 2026, 07:25:37 PM »
An update:
My onsite tech was able to connect the laptop running DMD directly to the PLC.  I used the IP Config utility to successfully (or so I thought) set the desired IP address and subnet mask.  I was then able to ping the PLC at:

10.101.50.14
255.255.0.0

NetEdit3 and DMD could now detect the PLC however, it was still displaying 0.0.0.0 PLC IP Address is invalid in DMD.  Similar in NetEdit3.

As seen in the attached screen grabs, I tried to update the PLC in DMD to the above IP address, but DMD wouldn't let me as it said there was an IP address conflict with a device at 10.101.50.14; I tried to set it to 10.101.50.51 (I knew that was an unused address).  DMD threw an error when I tried to update the IP address.

I then had my tech do the DIP switch hardware wipe of the network settings.  The reset seems to have worked, in that I can no longer ping the PLC at 10.101.50.14, but I can also no longer find it in IP Config, NetEdit3, or DMD.  I cannot ping the PLC at all, and it's no longer communicating with the touchscreens.

Feels like time to throw in the towel and start the RMA process.  Do I send the PLC back to AutomationDirect, or to Host for forensics?  Happy to do either but I'd really like to know what happened.  I do have a spare PLC on the shelf, so I can get a new unit out to the client while waiting for a return/replacement.



SceneryDriver

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3858
    • Host Engineering
Re: BRX has lost IP address
« Reply #11 on: February 09, 2026, 09:14:34 PM »
1. Have remote person set the IP address.
2. Have the remote person power cycle the PLC
3. Have the remote person verify the IP address
4. Use the Blink Error Light on the Select Link dialog to get a time frame for the VPN overhead.  The turnaround time shows up in the Enabled column.
5. Hit the Edit Link button on the Select Link dialog, select Port tab, Advanced Settings button, and make sure your Timeout is 2x of that turn-around time value for your Communication Link (or more, e.g. 40ms turnaround, make it 80ms or 100ms)
6. You just connect to the PLC - do NOT try to change the IP address using the IP address you are about to change


SceneryDriver

  • Jr. Member
  • **
  • Posts: 15
Re: BRX has lost IP address
« Reply #12 on: February 10, 2026, 06:04:37 PM »
1. Have remote person set the IP address.
2. Have the remote person power cycle the PLC
3. Have the remote person verify the IP address
4. Use the Blink Error Light on the Select Link dialog to get a time frame for the VPN overhead.  The turnaround time shows up in the Enabled column.
5. Hit the Edit Link button on the Select Link dialog, select Port tab, Advanced Settings button, and make sure your Timeout is 2x of that turn-around time value for your Communication Link (or more, e.g. 40ms turnaround, make it 80ms or 100ms)
6. You just connect to the PLC - do NOT try to change the IP address using the IP address you are about to change


We've basically done exactly what you describe.  We used IP Config on a local PC connected directly to the PLC to set the IP address.  It would respond to pings and the expected IP address successfully.

However, there was no way to connect to the PLC in DMD.  The PLC wouldn't respond when I tried to edit the link to the IP address set via IP Config, and DMD saw a new PLC at 0.0.0.0  Trying to connect to it and give it any IP address was unsuccessful, with the error message posted above.

After the hardware reset of the network settings, I can no longer set the IP address in IP Config, or any other way.  It doesn't even show up as a new unconfigured unit that needs its network settings.

It's still running its program, just not communicating with the outside world. 

Question: If I send out the spare unit I have on the shelf, I'd like pre-load the program and pre-configure the netowrk settings.  Will I have issue loading the program since the program is expecting an analog module to be installed, and my replacement won't have one (until it's all put together onsite)?


SceneryDriver

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3858
    • Host Engineering
Re: BRX has lost IP address
« Reply #13 on: February 11, 2026, 08:30:25 AM »
However, there was no way to connect to the PLC in DMD

Is that locally or remotely or both?  Being able to connect locally tells us that the IP setup is valid and working locally.

SceneryDriver

  • Jr. Member
  • **
  • Posts: 15
Re: BRX has lost IP address
« Reply #14 on: February 11, 2026, 01:00:52 PM »
However, there was no way to connect to the PLC in DMD

Is that locally or remotely or both?  Being able to connect locally tells us that the IP setup is valid and working locally.

We did everything locally, using a laptop with a direct connection to the PLC through Ethernet, and a remote connection via Chrome remote Desktop over wifi.  IP config worked, but kinda seemed not to - DMD couldn't see the PLC as anything but 0.0.0.0 even after giving the PLC it's IP address with IP Config.



SceneryDriver