I connected the sensor to an analog input configured as +/- 10v, and triggering at 0.5 &-0.5volts, which works great at the current flow rate of 100 gpm. Getting about 20 pulses per gallon, which is exactly double what I got with the digital input. I'm thinking this is going to be generating too many pulses at about 400 gpm, so i might have to block the negative pulses. What I don't understand is how this sensor worked at all before, as the amplitude of the pulses is never more than 3vdc, according to my osciloscope.