News:

  • October 15, 2026, 12:51:43 AM

Login with username, password and session length

Author Topic: Comm Error unlocking PLC  (Read 38184 times)

mhw

  • Hero Member
  • *****
  • Posts: 250
Comm Error unlocking PLC
« on: June 12, 2025, 09:47:06 AM »
I was trying to connect to an old D0-05 PLC using DS6 with a serial connection. Configuring the K Sequence link gives a green light. Trying to connect to the PLC then gives the error message, "Comm Error unlocking PLC". I tried both ports 1 and 2 with the same result. I verified that I can connect to a different 05 that I found at my office. Unfortunately I was unable to find an ECOM card to try on the unresponsive PLC. The program in the PLC is still working and rebooting the PLC or changing the mode switch did not help.
Any ideas what I can try?

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3850
    • Host Engineering
Re: Comm Error unlocking PLC
« Reply #1 on: June 12, 2025, 10:00:43 AM »
You might try looking at the Link Info page for that Comm Link to get some idea of the specific issues/errors being reported.  There should have been more detail in the message box as to why it could not unlock the PLC.

From DSLaunch's Link's group, you should be able to click (right-click?) to get a menu or button to get Link Info with error details.

Let us know what you see.

rlp122

  • Sr. Member
  • ****
  • Posts: 92
Re: Comm Error unlocking PLC
« Reply #2 on: June 15, 2025, 12:04:41 PM »
Try DirectNET.  On some older DL05's the comm port can become unresponsive to K-sequence.  If you can get it to connect, update the firmware asap.

mhw

  • Hero Member
  • *****
  • Posts: 250
Re: Comm Error unlocking PLC
« Reply #3 on: October 09, 2025, 08:02:57 AM »
Thanks for your responses.
I finally was able to get back to that site. This time it connected without any problems. Not sure what the issue was.