Trouble with Modbus RTU over 485 to Siemens V20
« on: October 29, 2024, 02:35:32 PM »
I'm having trouble polling from a BRX to a Siemens V20 over 485.   .XferCount increments but no values are written to the target range in BRX (I can even overwrite registers in range, so I know it's not just writing zeros).  I can communicate from a laptop to the V20 via FTDI USB-485 adaptor, and I get good non-zero data.

I tried running a PC Modbus slave and letting the BRX target the PC, and I never get an RX light on the PC from the BRXs TX nor an RX light on the BRX indicating a response.

Port setup:  9600-O-8-1 (tried both terminated and not)

Anyone successfully do this?
I retract my earlier statement that half of all politicians are crooks.  Half of all politicians are NOT crooks.  There.

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6154
  • Yes Pinky, Do-more will control the world!
Re: Trouble with Modbus RTU over 485 to Siemens V20
« Reply #1 on: October 29, 2024, 03:26:32 PM »
Don't have the Siemens thing, but I went between two BRX -18s. RS485, 9600-8-1-O. Read 10 holding registers. Write to N0. Worked perfectly first time. Not sure what to suggest.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO