Author Topic: BRX multi PLC System rebooting itself for no reason  (Read 12244 times)

clyleadams

  • Newbie
  • *
  • Posts: 7
BRX multi PLC System rebooting itself for no reason
« on: February 03, 2024, 09:31:47 PM »
So this has happened on two different recontrol installations.

I use multiple BRX PLC's in a machine system with one PLC in each machine section (5 total) and one in the main drive cabinet.  in the system event log,  there are multiple entries that indicate the system has turned off and then back on (which may be less than one minute apart in the system log.   so the PLC is actually rebooting itself for some reason and it doesnt appear to be a hardware watchdog timeout.

Also,  there are 7 C-more touchscreens on the same network which may or may not be trying to communicate with the specific PLC?

any ideas on what this may be?

I am attaching an event log from another controller that does the same thing occassionally but doesnt cause a problem.

any help would be appreciated. 

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: BRX multi PLC System rebooting itself for no reason
« Reply #1 on: February 03, 2024, 09:42:20 PM »
So this has happened on two different recontrol installations.

I use multiple BRX PLC's in a machine system with one PLC in each machine section (5 total) and one in the main drive cabinet.  in the system event log,  there are multiple entries that indicate the system has turned off and then back on (which may be less than one minute apart in the system log.   so the PLC is actually rebooting itself for some reason and it doesnt appear to be a hardware watchdog timeout.

Also,  there are 7 C-more touchscreens on the same network which may or may not be trying to communicate with the specific PLC?

any ideas on what this may be?

I am attaching an event log from another controller that does the same thing occassionally but doesnt cause a problem.

any help would be appreciated.

"Main drive cabinet"? A VFD? First concern would be noise. Might be best at contact us at support@hosteng.com
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

clyleadams

  • Newbie
  • *
  • Posts: 7
Re: BRX multi PLC System rebooting itself for no reason
« Reply #2 on: February 03, 2024, 10:39:39 PM »
The system has been installed since 2020 - no noise issues.  this problem cropped up in the last two weeks.  we isolate the 24V from the Power Components

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: BRX multi PLC System rebooting itself for no reason
« Reply #3 on: February 03, 2024, 11:02:40 PM »
The system has been installed since 2020 - no noise issues.  this problem cropped up in the last two weeks.  we isolate the 24V from the Power Components

Maybe some kind of new network traffic that is causing the PLC some heartburn. Still probably be best to contact us. We can work more closely with you to figure it out.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

clyleadams

  • Newbie
  • *
  • Posts: 7
Re: BRX multi PLC System rebooting itself for no reason
« Reply #4 on: February 03, 2024, 11:35:15 PM »
I have emailed support.
Thanks

rlp122

  • Sr. Member
  • ****
  • Posts: 92
Re: BRX multi PLC System rebooting itself for no reason
« Reply #5 on: February 11, 2024, 11:07:21 PM »
The system has been installed since 2020 - no noise issues.  this problem cropped up in the last two weeks.  we isolate the 24V from the Power Components

Just because noise hasn't shown up as an issue historically doesn't mean that it doesn't exist.  I can't count the number of systems where the customer swore up and down there was no noise present until I got on site and dug the oscilloscope out.  Surprise!  It's full of noise.

Sticking a scope on the power and comms is the only way to be sure.