News:

  • November 23, 2026, 03:40:34 AM

Login with username, password and session length

Author Topic: BRX Hardware Watchdog Timeout  (Read 22635 times)

JeffS

  • Hero Member
  • *****
  • Posts: 116
BRX Hardware Watchdog Timeout
« on: September 29, 2023, 05:50:26 PM »
I have a few PLCs that are pretty consistently triggering the hardware watchdog timeout.  Attached are the system logs for the two PLCs.  Is there anything I can do to narrow down what could be causing this?   For the Test BRX Maestro it has nothing wired up to any of the cards attached to the BRX PLC.  On my test BRX I plan to unplug the connectors on every card so they don't have external power, just to see if that affects the hardware timeout occurrence.

Carnegie PLC: 2.9.6 OS, 1.1.0 Booter

Test PLC: 2.9.7 OS, 1.1.0 Booter

What can I do to help narrow this down to a particular card or whatever is actually causing the timeout?

Thanks,
Jeff
« Last Edit: September 29, 2023, 05:56:45 PM by JeffS »

Greg

  • HostTech
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 702
  • Hmmm...
    • Host Engineering, Inc.
Re: BRX Hardware Watchdog Timeout
« Reply #1 on: October 02, 2023, 12:49:37 PM »
Normally, a hardware watchdog trigger is caused by something physical like:
  • Radiated electrical noise (e.g. VFDs nearby?)
  • I/O wiring/routing in parallel with high voltage
  • No snubbers on relay I/O
  • Dirty power and/or brown outs
  • Changes/events to PLC program and/or the machine process
The System Data Word, DST385 ($WatchdogReboots) shows a count of how many times it has rebooted.
DST400-409 contain codes for us (Host Engineering) that may help narrow down what is happening. Can you post those?
There are two types of people in the world; those that can extrapolate from incomplete data sets.

JeffS

  • Hero Member
  • *****
  • Posts: 116
Re: BRX Hardware Watchdog Timeout
« Reply #2 on: October 04, 2023, 11:07:35 AM »
Attached are some screen shots of the contents of DST385 and DST400-409.  I have this happening on another PLC in the field as well at a separate location.
Where DST385 is 0 is because the PLC had dropped out of run after reaching 10, which each of these PLCs had all done at the time I logged in to get the data.

Greg

  • HostTech
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 702
  • Hmmm...
    • Host Engineering, Inc.
Re: BRX Hardware Watchdog Timeout
« Reply #3 on: October 05, 2023, 10:35:36 AM »
Attached are some screen shots of the contents of DST385 and DST400-409.  I have this happening on another PLC in the field as well at a separate location.
Where DST385 is 0 is because the PLC had dropped out of run after reaching 10, which each of these PLCs had all done at the time I logged in to get the data.
The codes in DST400-409 look normal. But DST385 ($WatchdogReboots) = 0 is a bit troublesome.

Does this ever increment?

Also, since these all look normal (except for the DST385), what are these values?
- DST410 ($ModeChngFailed)
- DST411 ($DebugTrapAddr)
- DST412 ($AssertCode)
There are two types of people in the world; those that can extrapolate from incomplete data sets.

JeffS

  • Hero Member
  • *****
  • Posts: 116
Re: BRX Hardware Watchdog Timeout
« Reply #4 on: October 05, 2023, 12:55:45 PM »
Here are the other values you wanted.

You can see that DST385 does increase as it appears all the PLCs have tripped watchdog another couple times since I put them back in RUN. Seems I forgot to put the Test PLC back into run, so it is still showing 0 for watchdog reboot count.

Thanks,

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: BRX Hardware Watchdog Timeout
« Reply #5 on: October 05, 2023, 03:27:57 PM »
Here are the other values you wanted.

You can see that DST385 does increase as it appears all the PLCs have tripped watchdog another couple times since I put them back in RUN. Seems I forgot to put the Test PLC back into run, so it is still showing 0 for watchdog reboot count.

Thanks,

The value in DebugTrapAddr suggests that this was an OS crash.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

JeffS

  • Hero Member
  • *****
  • Posts: 116
Re: BRX Hardware Watchdog Timeout
« Reply #6 on: October 05, 2023, 04:50:15 PM »
So looking at System Status I did notice that I had lots of DLWX failed comms on one of the PLCs.  Would these cause the OS to crash?

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: BRX Hardware Watchdog Timeout
« Reply #7 on: October 05, 2023, 05:03:48 PM »
So looking at System Status I did notice that I had lots of DLWX failed comms on one of the PLCs.  Would these cause the OS to crash?

Honestly nothing should ever cause it to crash, but failure conditions are always the harder thing to test.

I don't have a map file from the exact build you're running, but that address does point to some network stuff in some builds. The only way to be certain what's happening is to give you a new build of the OS with the map updated, then we can know where in the code it was when it went on walkabout. That doesn't always tell us what we need to know, but it's a start.

Not to shirk responsibility, but the ever changing network environment makes network issues a moving target. The issue we had last year where TCP servers (generally Modbus) were locking up ended up being a bug that I'm 90% sure had been in the stack since day 1, but changing network hardware (radios in this case) exposed it 10 years after initial Do-more release. Since there is always something new happening, sometimes thing just pop up. All you can do is deal with it when it happens, but it makes us scratch our heads at times.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

JeffS

  • Hero Member
  • *****
  • Posts: 116
Re: BRX Hardware Watchdog Timeout
« Reply #8 on: October 05, 2023, 05:13:23 PM »
Ok, on one of the PLCs I patched this code to stop the DLWX comms to see if that stops the watchdogs. 

I am willing to try a new OS build to help figure this out as well.

JeffS

  • Hero Member
  • *****
  • Posts: 116
Re: BRX Hardware Watchdog Timeout
« Reply #9 on: October 05, 2023, 06:16:47 PM »
I also sat watching the Status for a while and noticed this popping up on occasion.  Something to worry about, or possibly related?  Seems to correspond to some ping instructions failing.

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: BRX Hardware Watchdog Timeout
« Reply #10 on: October 05, 2023, 07:33:53 PM »
I also sat watching the Status for a while and noticed this popping up on occasion.  Something to worry about, or possibly related?  Seems to correspond to some ping instructions failing.

Possibly related. That is the TCP stack getting its panties in a bunch, generally due to something not working as expected.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

JeffS

  • Hero Member
  • *****
  • Posts: 116
Re: BRX Hardware Watchdog Timeout
« Reply #11 on: October 06, 2023, 05:53:45 PM »
Ok, leaning more toward the panic thing being the issue.  After stopping the DLWX errors I still got 3 more hardware watchdogs in roughly 24 hours.  What do you need me to do in order to help narrow this issue down?

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: BRX Hardware Watchdog Timeout
« Reply #12 on: October 09, 2023, 11:37:24 AM »
Ok, leaning more toward the panic thing being the issue.  After stopping the DLWX errors I still got 3 more hardware watchdogs in roughly 24 hours.  What do you need me to do in order to help narrow this issue down?

Panics only happen when the stack gets something it isn't sure how to deal with. That suggests some unusual network traffic.

I'm eyeballs deep in some stuff right now, but let me see if I can get a beta build together with an up-to-date map file. That allows me to translate the panic address to the source function that is complaining. Once we know that, we'll figure out what's next. It generally involves peeling the onion with debug builds that dump diagnostic info.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

JeffS

  • Hero Member
  • *****
  • Posts: 116
Re: BRX Hardware Watchdog Timeout
« Reply #13 on: October 10, 2023, 12:19:49 PM »
So, messing with this some more. 

At the locations where these BRX PLCs are having the issues, only the PLC running this specific program is having the watchdog timeouts, while 3 other BRX PLCs on the same network are not having this issue.

On my Test BRX I stopped running any programs that performed any comms actions and I am still getting the hardware watchdogs.  On this same network I loaded this same program to a BRX without the I/O modules and it hasn't had the watchdog timeouts.  I am now installing the I/O to see if this PLC starts getting watchdog timeouts.  I will let you know.



« Last Edit: October 10, 2023, 12:24:48 PM by JeffS »

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: BRX Hardware Watchdog Timeout
« Reply #14 on: October 11, 2023, 11:08:06 AM »
If you can reliably duplicate it on a test system, we just need to dupe it here and fix it.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO