VFD's create harmonics out the wazoo. Also VFD's/motors must be grounded per the manufacturers specifications. For GS drives, this means the motor ground must go to the drive chassis. Bonding the motor to a common ground will cause noise issues. In addition the longer the drive leads to the motor, the more noise you will get due to the increased reflections of the carrier wave. Plus you have the whole impedance matching of the supply transformer to the drive to consider.
VFD's are complicated beasts and everything matters when you are trying to mitigate noise issues with them. Adding EMI filters and Line reactors is often just a part of a more complex solution.
BobO has it right with the speed of the input transistor or lower capacitance in the input circuit. Both of these items are something that is different in BRX. When we designed these input circuits we wanted to mitigate the super high inrush current that the older AC input designs had. We also wanted a high enough speed that it would match up with the fastest AC sensors that ADC currently sold. Tradeoffs...