News:

  • November 23, 2026, 01:58:38 AM

Login with username, password and session length

Author Topic: Error when writing to BRX  (Read 30916 times)

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: Error when writing to BRX
« Reply #15 on: April 26, 2023, 04:41:33 PM »
There anything I can look at to try and narrow it down?

Thanks

Not really. The big help to us would be if you could dupe it semi-reliably. Barring that, we can do a special build of the firmware that adds in some additional diagnostics that might give us an idea of where the scan spike is coming from.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

JeffS

  • Hero Member
  • *****
  • Posts: 116
Re: Error when writing to BRX
« Reply #16 on: April 28, 2023, 12:57:14 PM »
So far this morning I have consistently(12 times in a row so far) gotten the "Unable to determine if OLD to New project transition has complete." error.  Always happens during the ROM update phase.  If I try to write again pretty quickly after the error I get "Waiting for previous ROM operation to complete" and takes 15-20 seconds to clear.

So far as reproducing... My current setup and the current change I am trying to write the PLC is consistently giving me this error.  What can I do to shed some light on the issue?


franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3856
    • Host Engineering
Re: Error when writing to BRX
« Reply #17 on: April 28, 2023, 01:04:17 PM »
Is this a RUN mode edit (i.e. PLC is staying in RUN mode while the PROGRAM is being written), or does this Write have a SYSCONFIG change, so the Designer Write to PLC Dialog changes the PLC to PROGRAM mode before it initiates the Write to PLC?

JeffS

  • Hero Member
  • *****
  • Posts: 116
Re: Error when writing to BRX
« Reply #18 on: April 28, 2023, 01:13:37 PM »
Currently what I am testing is the RUN mode edit.  Sticking to it since I can make it repeat currently, the problem has been sporadic previously where it might fail 5 times then work.  So far it hasn't worked yet.

JeffS

  • Hero Member
  • *****
  • Posts: 116
Re: Error when writing to BRX
« Reply #19 on: April 28, 2023, 01:38:02 PM »
Also I tried to do a compare to list off the differences I was trying to write and ... says programs match.  Disconnected and connected with another instance of Do-more to see what the PLC showed, and it has the bits of code I added along with documentation.  So I'm not sure what it thinks is different and is failing to write to the PLC at this point. 

When I connect back with my saved program it still indicates the rungs I had changed(but are showing up in the PLC when I connect with a different instance) are different from the PLC.  And still fails the RUN mode update.

No idea if this matters, but this is the same program that has the duplicate nicknames for bits because my nicknames are at max character length(https://forum.hosteng.com/index.php?topic=3786.0).  Also I am using 62514/65536 of the program memory.

And I can confirm that if I change something in the program and write the PLC, even though it gives the "Unable to determine if OLD to New project transition has complete." error the changes are being written.  Program still indicates the PLC and Software are different though.
« Last Edit: April 28, 2023, 01:40:19 PM by JeffS »

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3856
    • Host Engineering
Re: Error when writing to BRX
« Reply #20 on: April 28, 2023, 02:53:42 PM »
Next time you write to the PLC, bring up a Data View and look at
ST200:B in HEX/BCD format
It should be 0x00 after all the Project updates to FLASH are finished.

We poll that value at the end of the Write Project to PLC process, looking for it to go to 0x00.  We give it 60 seconds, then we error-out if it stays non-zero.

What are you seeing for this in Data View?

JeffS

  • Hero Member
  • *****
  • Posts: 116
Re: Error when writing to BRX
« Reply #21 on: April 28, 2023, 03:04:23 PM »
Looks like it takes another 49 seconds after the error before the contents zero back out.  Showed 0x04 for part of the update then 0x05 up to and past the error until it finally went to 0x00.

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3856
    • Host Engineering
Re: Error when writing to BRX
« Reply #22 on: April 28, 2023, 04:18:33 PM »
ST200 is PROGRAM ROM Update (0x01)
ST201 is SYSCONFIG ROM Update (0x02)
ST202 is DOCUMENTATION ROM Update (0x04)

so
0x04 is just DOCUMENTATION
0x05 is DOCUMENTATION and PROGRAM (0x04 | 0x01)
0x00 is none

JeffS

  • Hero Member
  • *****
  • Posts: 116
Re: Error when writing to BRX
« Reply #23 on: April 28, 2023, 04:33:15 PM »
Ok, so it is taking extra long to update the program and documentation ROM?  Much more so than the program anticipates at maximum?

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3856
    • Host Engineering
Re: Error when writing to BRX
« Reply #24 on: April 28, 2023, 04:41:45 PM »
EDIT (see below)

Yes.  It polls those values, looking for the value 0x00, for up to 60 seconds.
But you're seeing that it's another 49 seconds after that, so it's taking 109 seconds to write the Project to ROM.

FYI, you definitely need to wait for ST200:B to get to 0x00 before trying any other Project Writes.  The 60 second "max" was just a guess.  With huge programs with huge scan times, with large documentation files, doing RUNTIME edits, it obviously can take longer than 60 seconds.  We can definitely tweak that.

But I don't think this is your issue (could be?), especially if you try another Write to PLC while the previous one is still updating flash!


SORRY - 60 seconds is the maximum amount of time we wait BEFORE we start a NEW Write to PLC.  Designer makes sure none of the PREVIOUS ROM updates are occurring BEFORE it starts a NEW Write Project to PLC.  If it takes longer than 60 seconds, Designer does not try to write the Project - it just tells you to try again.
« Last Edit: April 28, 2023, 04:55:58 PM by franji1 »

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3856
    • Host Engineering
Re: Error when writing to BRX
« Reply #25 on: April 28, 2023, 04:43:34 PM »
As a work-around, just do PROGRAM mode changes.  This may mess with your logging file entries, but the integrity of the project in the PLC flash is crucial.