News:

  • November 23, 2026, 02:09:28 AM

Login with username, password and session length

Author Topic: Should Reset Range override off-delay timer?  (Read 8289 times)

PLCwannabe

  • Hero Member
  • *****
  • Posts: 208
Should Reset Range override off-delay timer?
« on: February 28, 2023, 05:42:32 PM »
 I have a program where the first rung in Main is an e-stop button input that resets the full range of relay outputs (Y0-Y31). I noticed today that this rung is not resetting a relay output that is being held in by an off-delay timer. Is this normal?

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: Should Reset Range override off-delay timer?
« Reply #1 on: February 28, 2023, 06:03:12 PM »
I have a program where the first rung in Main is an e-stop button input that resets the full range of relay outputs (Y0-Y31). I noticed today that this rung is not resetting a relay output that is being held in by an off-delay timer. Is this normal?

Last one wins. Stick your estop in the bottom of scan task.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

PLCwannabe

  • Hero Member
  • *****
  • Posts: 208
Re: Should Reset Range override off-delay timer?
« Reply #2 on: March 01, 2023, 12:24:41 PM »
Makes sense now.

PLCwannabe

  • Hero Member
  • *****
  • Posts: 208
Re: Should Reset Range override off-delay timer?
« Reply #3 on: March 05, 2023, 05:32:38 PM »
Can I use the $BottomofScan to override a PID loop that is in auto, by writing directly to the analog register? (RY0)

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: Should Reset Range override off-delay timer?
« Reply #4 on: March 05, 2023, 06:00:31 PM »
Can I use the $BottomofScan to override a PID loop that is in auto, by writing directly to the analog register? (RY0)

That should work.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO