« on: December 05, 2022, 11:21:24 AM »
What do the vertical red/blue lines in a trend view mean? For a while, I've assumed that these indicated comms issues between the PC running DmD and the PLC. I'm seeing these now in a trend view where I suspect comms to be good between the PC and the PLC but all values shown on the trend view are coming from remote Modbus devices and I'm getting periodic MRX/MWX failures. I believe the network infrastructure from the PLC to the Modbus devices to be less than ideal.   

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3468
    • Host Engineering
Re: Vertical Red/Blue Lines in Trend View
« Reply #1 on: December 05, 2022, 01:02:05 PM »
They are Comm Link status, including status going on and off, which can happen during Program Writes, firmware updates, changes to the System/Memory Configuration.

Blue:
Link Error CLEARED
Link UNPAUSED (after editing a Comm Link)
Link ACTIVE (check/uncheck Link Active in Link Editor)
Status ON

Yellow:
Status OFF

Red:
Link INACTIVE
Link PAUSED (editing Comm Link)
Link ERROR (comm error)

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3468
    • Host Engineering
Re: Vertical Red/Blue Lines in Trend View
« Reply #2 on: December 05, 2022, 02:10:05 PM »
To see Comm Link log details, open up the Link Info dialog either by clicking on the Link name in the Status Bar or under PLC->Link Info menu item.


RBPLC

  • Hero Member
  • *****
  • Posts: 533
Re: Vertical Red/Blue Lines in Trend View
« Reply #3 on: December 05, 2022, 02:21:37 PM »
I'm guessing that seeing Transport Protocol Errors (appearing "randomly" and for very brief periods of time <1/2 second) could be a sign of potential network traffic issues. I'm also guessing that seeing a timeout for a sufficiently long period of time would also indicate that the same network conditions causing the timeout of the link would cause issues with the MRX/MWX functions. Are these true statements? 

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3468
    • Host Engineering
Re: Vertical Red/Blue Lines in Trend View
« Reply #4 on: December 05, 2022, 03:54:34 PM »
I'm guessing that seeing Transport Protocol Errors (appearing "randomly" and for very brief periods of time <1/2 second) could be a sign of potential network traffic issues.
Could be Noise (more likely), Runtime Edit, Firmware update.  Unless you have some kind of broadcast or bandwidth issues, noise is a potential comm issue.
Here's some general help on Ethernet, Panels, and Noise:
https://hosteng.com/FAQFiles/ECOM.htm#FAQ0045

Quote
I'm also guessing that seeing a timeout for a sufficiently long period of time would also indicate that the same network conditions causing the timeout of the link would cause issues with the MRX/MWX functions.
Network traffic, noise, runtime edit, firmware update - yes.