News:

  • August 02, 2026, 04:45:53 PM

Login with username, password and session length

Author Topic: IO Hardware Failure  (Read 6348 times)

Dmdtrain

  • Jr. Member
  • **
  • Posts: 11
IO Hardware Failure
« on: November 01, 2022, 01:48:01 PM »
Hello,

We had a power surge at a facility and two of our start/stop panels no longer are working. It's 205 series IO. We are failing to find what component is not working, so I was looking to see if anyone has seen something similar.

First thing we noticed was the EBC in one panel had a bad port so we replaced that and it came back onto the network.

Both panels are now connected to the network. I can ping the EBCs from the programming PC. Power looks good going to the IO. We tried swapping the base out D2-04BDC-1 and one of the input modules D2-08NDC3. No success with either of those components.

I cannot force outputs or see inputs turning on for those IO mappings.

Both panels feed to the same network switch along with 2 other panels that are working. The switch then makes it's way back to the main processor like all other panels.

Having a hard time racking my head around this one. Any suggestions are appreciated!!

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3838
    • Host Engineering
Re: IO Hardware Failure
« Reply #1 on: November 01, 2022, 02:07:47 PM »
Definitely post this one on ADC's Community website - you will get a lot more eyes looking at it and a lot of help.

https://community.automationdirect.com/

Dmdtrain

  • Jr. Member
  • **
  • Posts: 11
Re: IO Hardware Failure
« Reply #2 on: November 01, 2022, 02:12:10 PM »
Thank you I will do that.