News:

  • November 26, 2026, 02:52:59 PM

Login with username, password and session length

Author Topic: Saving Setpoint  (Read 9580 times)

dieseltwitch

  • Full Member
  • ***
  • Posts: 23
Saving Setpoint
« on: May 13, 2009, 03:41:12 PM »
How do I save set point changes made while the PLC is running into some type of long term memory that can be recalled after the plc loses power?
« Last Edit: May 13, 2009, 06:16:35 PM by dieseltwitch »

b_carlton

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 606
    • thePLCguy
Re: Saving Setpoint
« Reply #1 on: May 13, 2009, 06:29:48 PM »
Look up 'retentive ranges'. Unlike the Allen-Bradley processors, the AD processors would happily zero out everything on startup unless told otherwise. That's where 'retentive ranges' comes in. It just tells the processor what NOT to zero out. There are some ranges already included. Check to see if the registers you want are included. If not modify the ranges. Be careful though. Make sure you aren't assuming that some items start with zero. If included in the 'retentive range' it could be anything.
An output is a PLC's way of getting its inputs to change.