I have to agree with fiaranch. The thought of dropping 600 using dividing resistors and hooking it to a PLC input makes me a little nervous. Up to 50-100 volts, sure. But if the high value resistor above the PLC input shorts (unlikely) or the low value below the input opens (more likely fault), you won't like it. Those signal conditioners can be had with a couple thousand volts of isolation between the process signal and the PLC input signal, and if something were to fail in there, it would be more likely to simply stop working as opposed to putting 600 VDC on the PLC input terminals.