News:

  • November 23, 2026, 12:58:50 AM

Login with username, password and session length

Author Topic: Ethernet IO  (Read 7864 times)

mhw

  • Hero Member
  • *****
  • Posts: 250
Ethernet IO
« on: March 30, 2022, 08:48:45 AM »
I am converting an existing 260 PLC with a DoMore. There will be some Ethernet IO. I am trying to do some bench testing without having the remote bases connected. I have the box checked "CPU remains in RUN mode on slave error" and unchecked is "Slave must be online to enter RUN mode". The PLC will not go to run mode. It gives the following error, "IO Configuration Error - $IOConfigError (ST135)". I can clear this error, but it will come back every time I try to go to run mode.
This behavior is not what I expected. How about you? Is there a way that I can make it go to run without the remote bases?

Thank you,
Mike

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3856
    • Host Engineering
Re: Ethernet IO
« Reply #1 on: March 30, 2022, 09:09:02 AM »
Check the I/O System View when Online to the PLC to see all the specific I/O errors, not just the general ST135 bit.

mhw

  • Hero Member
  • *****
  • Posts: 250
Re: Ethernet IO
« Reply #2 on: March 30, 2022, 09:23:02 AM »
Quote
Check the I/O System View when Online to the PLC to see all the specific I/O errors, not just the general ST135 bit.
The ST135 is the only error. There are two warnings, ST152 and ST154.

mhw

  • Hero Member
  • *****
  • Posts: 250
Re: Ethernet IO
« Reply #3 on: March 30, 2022, 09:28:13 AM »
Sorry, I need to hear what you said and not what I want to hear. The problem was that my local base did not match the configuration.
Thanks for your help.

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3856
    • Host Engineering
Re: Ethernet IO
« Reply #4 on: March 30, 2022, 09:48:53 AM »
Sorry, I need to hear what you said and not what I want to hear. The problem was that my local base did not match the configuration.
Thanks for your help.

Glad you figured it out!