News:

  • November 23, 2026, 12:14:37 AM

Login with username, password and session length

Author Topic: Analog input max voltage  (Read 13452 times)

PLCwannabe

  • Hero Member
  • *****
  • Posts: 208
Analog input max voltage
« on: January 29, 2022, 10:20:43 AM »
Can 24vdc be applied directly to analog 0-10vdc channel to be used as digital input?

RBPLC

  • Hero Member
  • *****
  • Posts: 586
Re: Analog input max voltage
« Reply #1 on: January 29, 2022, 10:50:39 AM »
No. You'll most likely damage the module.

Controls Guy

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 3628
  • Darth Ladder
Re: Analog input max voltage
« Reply #2 on: January 30, 2022, 02:01:42 PM »
Time for a redneck voltage regulator.   Either put a resistor about double the input resistance in series, which will give an 8V on-level, or (better regulation),  a slightly smaller series resistor and a zener diode in parallel with the input.   Set your threshold at 6V maybe.
I retract my earlier statement that half of all politicians are crooks.  Half of all politicians are NOT crooks.  There.

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: Analog input max voltage
« Reply #3 on: January 30, 2022, 02:58:12 PM »
Time for a redneck voltage regulator.   Either put a resistor about double the input resistance in series, which will give an 8V on-level, or (better regulation),  a slightly smaller series resistor and a zener diode in parallel with the input.   Set your threshold at 6V maybe.

In voltage mode the input impedance is very high. I'd personally opt for the zener/resistor combo. I'm from the hills of East Tennessee, but even we have minimum (redneck) design standards.  ;)
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

Controls Guy

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 3628
  • Darth Ladder
Re: Analog input max voltage
« Reply #4 on: January 30, 2022, 03:18:45 PM »
I'm a Lone Star redneck.  Howdy!
I retract my earlier statement that half of all politicians are crooks.  Half of all politicians are NOT crooks.  There.

PLCwannabe

  • Hero Member
  • *****
  • Posts: 208
Re: Analog input max voltage
« Reply #5 on: January 30, 2022, 05:28:23 PM »
I did install a 12v Zener in series with the input, but that didn't work, I realize now I'll have to parallel it instead.


  Just to give a bit more background on this project, the input is being triggered by a 24vdc  PNP proximity switch (that is very hard to get to). When I connect this proximity switch output to a regular 24vdc input, the prox output voltage gets pulled down to about 3 vdc, which isn't enough to trigger the dc input. It's like the proximity switch can't supply enough current to trigger the input, which is why I'm trying to use the higher impedance analog input. I think I've got a faulty prox switch or dc input. I'll get a measurement on the dc input current tommorrow to confirm which part is faulty.

PLCwannabe

  • Hero Member
  • *****
  • Posts: 208
Re: Analog input max voltage
« Reply #6 on: January 30, 2022, 05:34:26 PM »
In voltage mode the input impedance is very high. I'd personally opt for the zener/resistor combo. I'm from the hills of East Tennessee, but even we have minimum (redneck) design standards.  ;)

I love to use up leftover parts on new projects, so some of my stuff definitely falls into the redneck category.
« Last Edit: January 31, 2022, 09:03:49 AM by franji1 »

Controls Guy

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 3628
  • Darth Ladder
Re: Analog input max voltage
« Reply #7 on: February 01, 2022, 11:03:34 AM »
Did you figure out which component wasn't working? 

My previous post was based on the assumption you were out of DI's rather than your actual case.   You'd probably need to size the resistor & zener differently and with more care for your scenario.
I retract my earlier statement that half of all politicians are crooks.  Half of all politicians are NOT crooks.  There.

PLCwannabe

  • Hero Member
  • *****
  • Posts: 208
Re: Analog input max voltage
« Reply #8 on: February 01, 2022, 02:03:19 PM »
The dc input module uses about 7mA/channel,which sounds about right, so I'm assuming the prox switch just can't supply enough current.
  My initial attempt with the 12.5v Zener in series is actually working great. The Zener is dropping 12.5vdc, and the prox switch is also dropping about 3vdc, which leaves about 9vdc at the input. No channel errors. I know this value will fluctuate somewhat with DC power supply voltage variations, but it's close enough.



Controls Guy

  • Internal Dev
  • Hero Member
  • ****
  • Posts: 3628
  • Darth Ladder
Re: Analog input max voltage
« Reply #9 on: February 02, 2022, 01:34:12 AM »
Yeah I was going to say, a series zener should be workable.   Not regulating per se, but still workable.
I retract my earlier statement that half of all politicians are crooks.  Half of all politicians are NOT crooks.  There.