Did you insert these rungs as a run-time edit? If so, the PLC doesn't count the transition back to run mode as a "first scan" so the values won't be loaded to configure the RTD card. Also, "first scan" is the only time the CPU looks at the values even if they were loaded. So try changing the mode to Program and back to Run using Directsoft or the mode toggle switch on the PLC or just do a power cycle. If it's still not working, verify that the correct values were written to V7700-V7706 by looking at them in a Data View.
Also, it's not relevant to troubleshooting this issue, but there is a newer way to configure analog modules than what's shown in the manual, and it's a lot cleaner. Look at the ANLGIN IBox in the online help for DirectSoft. I think you'll like it. I'm surprised AD hasn't fixed the manual yet.