News:

  • November 22, 2026, 07:28:48 AM

Login with username, password and session length

Author Topic: One Shot Trailing Edge Applied to Xxx Input - Not Working?  (Read 8050 times)

belias

  • Full Member
  • ***
  • Posts: 36
One Shot Trailing Edge Applied to Xxx Input - Not Working?
« on: January 05, 2022, 10:20:11 PM »
I've stared at this for 2 days now and I can't figure out what's going on.  I feel like I'm missing something obvious, so please be nice to me if it is...

This ladder logic comes from a task.  The top and bottom rungs work fine (the bottom run was actually just for my own testing).  The middle run that applies a trailing edge contact to the X38 input doesn't work.  Even when I provide a very slow (15 second) change to the X38 signal from ON to OFF, it still will not allow power flow.

As soon as I change the X38 to a C-bit and manually change it, it works fine.

Any idea what I'm missing?


RBPLC

  • Hero Member
  • *****
  • Posts: 586
Re: One Shot Trailing Edge Applied to Xxx Input - Not Working?
« Reply #1 on: January 05, 2022, 11:53:57 PM »
Two things:
1) What command is on the output side of the rung?
2) What does your ENTASK look like for this Task?

belias

  • Full Member
  • ***
  • Posts: 36
Re: One Shot Trailing Edge Applied to Xxx Input - Not Working?
« Reply #2 on: January 06, 2022, 11:11:55 AM »
Sorry...the picture was apparently too large to show the whole thing (re-sized below).  The output is a simple STRPRINT command.

The ENTASK is set in the Main program:

ST1 ($On)  ---->   ENTASK (Interval 0)

And it's not like this is an intermittent thing...every single time, it works perfectly for a change in the C-bit, but not for a change in the actual input (X-bit).

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: One Shot Trailing Edge Applied to Xxx Input - Not Working?
« Reply #3 on: January 06, 2022, 05:33:16 PM »
I put this code in a task exactly as shown, and it worked as expected. Only thing I can think of is the input isn't really doing what you think. You could try forcing it on then off and see if that fires the logic.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

ADC Product Engineer

  • Hero Member
  • *****
  • Posts: 270
Re: One Shot Trailing Edge Applied to Xxx Input - Not Working?
« Reply #4 on: January 07, 2022, 08:02:34 AM »
Put a counter on the rung under this one and use the same logic to trigger it.  As Bob said, I would bet that it doesn't increment when you think it is.