ROM or persistent memory space
« on: November 24, 2021, 10:17:42 AM »
Hi all:

Is there any user ROM or at least boot persistent memory on the H2-DM1E?  Do N,V, or R register values typically persist through restarts and power cycles?

I'd like to be able to write setpoints to a protected space and then ensure they get reloaded on 1st scan rather than risk having some unknown number upon restart.

Thanks!

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3858
    • Host Engineering
Re: ROM or persistent memory space
« Reply #1 on: November 24, 2021, 10:21:10 AM »
In all Do-more PLCs, the Image Register RAM is battery backed, so any elements/ranges marked as "retentive" will retain their values after a power loss.  Non-retentive values will be 0 after power returns.

It's a 10 year battery, so it will need to be replaced at some point (when you have power applied - there's no short term super-cap  ;D).

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3858
    • Host Engineering
Re: ROM or persistent memory space
« Reply #2 on: November 24, 2021, 10:26:49 AM »
Here's a screen shot of the default Memory Configuration.  Most blocks and heap items are fully retentive, but you can make a sub-range of a block be retentive or not.  For example, I/O is NOT retentive (X, Y, WX, WY, RX, RY) since even after a power cycle the PLC reads the latest inputs and in RUN mode the logic determines the desired output state after the 1st scan.

willpoll

  • Sr. Member
  • ****
  • Posts: 57
Re: ROM or persistent memory space
« Reply #3 on: November 24, 2021, 10:29:58 AM »
That works.  Thanks Franji1!