Not sure if this helps, but you can use Ctrl+Mouse Wheel to zoom in and out to a specific time/range wherever your mouse pointer is pointing (think Google Maps).
Ooh, that is cool! Wasn't aware of that one. Already using!
My beef with trend view has to do mostly with time increments. I don't like the random column durations you get with the default setting, nor the random default line times.
Since the line and tick settings don't change as you change time scaling, the user needs the number of columns to be highly composite, so that the column width is most likely to remain sane as you change time scale, so most desirable would be 12 or 24 columns (like why there are 24 hours in a day, 60 minutes in an hour, 12 inches in a foot, 36 inches in a yard, etc.). Since DMD specifies the column count indirectly as N
lines + 1, then it would be ideal for lines to be adjustable up to at least 11 or 23, rather than the current max of 10. With a max of 10, the best available setting for lines is 5, to give a column count of 6, which isn't bad.
Second, once you do get a good increment width, the actual column times are datumed on a random basis (probably based on when the trend was enabled), so the line time will be 10:29:06 or something random. Better to reconcile the line time to some multiple or divisor of the column duration, like if the column durations are 10 seconds, justify a line to the minute strike.
Also, trends can easily span days, and I don't believe there is anywhere on screen (without clicking for a snapshot) that identifies what day's 10:29:06 you're looking at, so maybe add the day and date at the bottom of the trend, at least as an option.
Might be better to have the user just set the column width in time duration per column and then either adjust that setting or column count when scaling the trend overall.
Thanks!