News:

  • October 16, 2026, 08:11:41 AM

Login with username, password and session length

Author Topic: BRX Pings failing  (Read 7613 times)

JeffS

  • Hero Member
  • *****
  • Posts: 115
BRX Pings failing
« on: July 22, 2021, 06:17:57 PM »
So in one of my projects, I use the PLC to manage the IP addresses of some connected VFDs.  In some of my logic 2 VFDs can have the same IP address, and I just disconnect one in order to sort it out.  The problem I am having is that I change the first VFD's address (.17.72) to something new(.19.5) and then when I plug in the second VFD that has the same IP as the one I just changed previously (.17.72) the ping I perform from the BRX fails.  I can ping this drive from other devices on the network just fine, but the BRX keeps failing.

If I power cycle the BRX it will ping the device (.17.72).  It will also find the device after sitting for 10-15 minutes.

Firmware 2.8.6
Booter 1.0.10
FPGA 1.15
Hardware 8A3A 

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6177
  • Yes Pinky, Do-more will control the world!
Re: BRX Pings failing
« Reply #1 on: July 23, 2021, 12:57:58 PM »
Sounds almost like an ARP record is involved. Power cycling clears it, or after some time it ages out. I wouldn't have guessed ping would be affected by ARP, but maybe.

Not really sure what to do about it. Duplicating IP addresses is kinda on the edge to start with, and I routinely have similar issues when I shuffle addresses like that.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

JeffS

  • Hero Member
  • *****
  • Posts: 115
Re: BRX Pings failing
« Reply #2 on: July 23, 2021, 01:42:52 PM »
Is the ARP cache something stored in the BRX?  Possible to clear it for a specific IP, or the entire cache?

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6177
  • Yes Pinky, Do-more will control the world!
Re: BRX Pings failing
« Reply #3 on: July 23, 2021, 02:29:53 PM »
Is the ARP cache something stored in the BRX?  Possible to clear it for a specific IP, or the entire cache?

It's in the IP stack and not directly accessible by you, or even me for the matter. I have modded the stack before and ended up re-releasing firmware because I did things with unexpected side effects.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO