I have an application being commissioned where I was going to use the internal port for remote programming access (and HMI if used in future), and a Modbus/TCP client at the site is transmitting requests to an ECOM on a separate subnet (buying EX's now but this is a leftover LT).
The client and I could both ping the LT, but it wouldn't respond to Modbus queries. I swapped the IP addresses between the internal and POM ports and the internal one works fine for Modbus. Modbus/TCP is enabled/checked, 10 sessions, port 502. The POM works fine for DM protocol for programming.
I've done this config many many times with no issue, and don't remember ever having to configure anything to make it work. Is this POM semi-faulty or what? Very weird.