News:

  • November 23, 2026, 09:35:54 AM

Login with username, password and session length

Author Topic: BX-Serio Module ASCII  (Read 6877 times)

RBPLC

  • Hero Member
  • *****
  • Posts: 586
BX-Serio Module ASCII
« on: December 01, 2020, 08:53:55 PM »
Does the BX-Serio module support Modbus ASCII and generic ASCII (used with STREAMIN and STREAMOUT) or just Mobus ASCII?

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: BX-Serio Module ASCII
« Reply #1 on: December 02, 2020, 12:11:49 AM »
Does the BX-Serio module support Modbus ASCII and generic ASCII (used with STREAMIN and STREAMOUT) or just Mobus ASCII?

It does not support Modbus ASCII natively, but yes, it does support STREAMIN/STREAMOUT, and the CHECKSUM instruction will do the CRC16 required for Modbus frames. The SERIO ports are essentially identical to the built-in port.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

RBPLC

  • Hero Member
  • *****
  • Posts: 586
Re: BX-Serio Module ASCII
« Reply #2 on: December 02, 2020, 05:53:04 AM »
Thanks.

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3857
    • Host Engineering
Re: BX-Serio Module ASCII
« Reply #3 on: December 02, 2020, 07:18:46 AM »
Here's an article w/video from Automation Direct's Community website showing how to do Modbus ASCII in Do-more.  It's easy to translate the "onboard" serial port to the SERIO module (Host designed it to make it very easy to move from port to port using "devices").

https://community.automationdirect.com/s/article/VIDEO-Do-more-BRX-Modbus-ASCII-Protocol