I could really use some help with this. I am on-site, 1,000 miles from home, and my customer is waiting for me to resolve this issue. I was on the phone with A/D tech support multiple times yesterday and got nowhere.
I have a BX-DM1E-10ED23-D that is sending 19.2mA from WY0 when there is a value of 6553 in the output register. It should measure 4.0mA. A value of 32767 yields 31.7mA.
This has been verified with multiple meters and I have connected several different devices to be sure the field device isn't causing this. I have attached a table that shows measured mA at various output values.
To eliminate wiring or interference issues, I removed the PLC from the enclosure and have it sitting on a desk, powered from a different 24VDC supply. The analog output is the only I/O wired at this time. I also cleared all of the PLC memory and re-flashed the firmware. This had no impact on the results. Normally, I would just RMA the unit, thinking there is something wrong with the analog output...
HOWEVER, I when I attach a BX-4AD4DA-3 analog combo card,
all of its outputs exhibit the exact same behavior! Could the problem just be the CPU? Is it capable of causing the add-on module to do this?

Best case, I get A/D to overnight a CPU for arrival Tuesday. I need to be confident that it will solve the problem, as the customer is waiting.

Any ideas would be appreciated.