News:

  • November 25, 2026, 07:22:10 PM

Login with username, password and session length

Author Topic: BX-DMIO-M-D and HSIO  (Read 6461 times)

jcb

  • Full Member
  • ***
  • Posts: 41
BX-DMIO-M-D and HSIO
« on: July 28, 2020, 03:43:58 PM »
I just figured out that I can't use an HSIO module on remote IO which is a bummer.

We can still use the old school H4-EBC's with the ERM and a H2-Do-more so i was kind of surprised I couldn't do it with the newer stuff?

Any plans to get this working? I only have one more open spot on my Base PLC but will be out of modules after that. This is a new build so I'm probably going to shift the 6 32 bit I/O modules over to the DMIO and put it in the same rack so I don't run into a problem later if we add a few more encoders.

What are other guys out there doing once you run out of I/O modules on your main unit and need to add High Speed Counters.

Thanks
John.



BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6180
  • Yes Pinky, Do-more will control the world!
Re: BX-DMIO-M-D and HSIO
« Reply #1 on: July 28, 2020, 04:02:04 PM »
I just figured out that I can't use an HSIO module on remote IO which is a bummer.

We can still use the old school H4-EBC's with the ERM and a H2-Do-more so i was kind of surprised I couldn't do it with the newer stuff?

Any plans to get this working? I only have one more open spot on my Base PLC but will be out of modules after that. This is a new build so I'm probably going to shift the 6 32 bit I/O modules over to the DMIO and put it in the same rack so I don't run into a problem later if we add a few more encoders.

What are other guys out there doing once you run out of I/O modules on your main unit and need to add High Speed Counters.

Thanks
John.

The HSIOx class of module is a much different technology than CTRIOs. Supporting them in remote bases is not viable without significant restrictions. We chose not to support H4-EBC in Do-more's Ethernet I/O because it requires features in the EBC100 that are not available on the EBC.

Most users use a BRX CPU as I/O and comm to it with Modbus/TCP or DLRX/WX.
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO

jcb

  • Full Member
  • ***
  • Posts: 41
Re: BX-DMIO-M-D and HSIO
« Reply #2 on: July 28, 2020, 07:04:55 PM »
Thanks Bob.

I just moved the 6 discrete modules over to a DMIO in the same panel and am pulling control wires to the Encoder cabinet. I now only have 2 Local modules on the Main PLC Brick so I should be fine moving forward on this project. 

Thanks Again.
John.